    Daikin Fan Fault



    Hi Guys, visited a Daikin ZMX52HV!NB with fan continuosly running on the outdoor unit when the indoor units switched off (split system).
    Checked Gas ok. System runs in heating mode but not in cooling mode. System runs in forced cooling ok. Any ideas???

    Thanks



  2. #2
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Daikin Fan Fault

    Not familiar with exact model number but from memory similar unit in Australia 4MX80HVEA had 240 condenser fan motor with two relays one for high speed and one for low speed.

    Possible cause for your problem, contacts welded on high or low speed relays on PCB.

    Is that a multi split unit?

  3. #3
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin Fan Fault

    Comon here with small panasonic splits. Some panasonics have a dumb out door unit, all controls are in the indoor unit.
    What happens with the panasonics here is that in order to fit everything in the indoor PCB and make it quieter, they started using a tiny solid state relay which sometimes fails.
    edit: although if you've got a bigger system maybe the fan control is in the outdoor unit and repairable.
    You need to find out what relay powers the fan, cut power to the unit and check the n/o contacts for fan switching, if you have a circuit, then the relay is fried because you shouldn't have a circuit when the power is off..
    Last edited by paul_h; 06-11-2007 at 10:42 AM.

  4. #4
    Join Date
    Jul 2007
    Location
    staffordshire
    Posts
    22
    Rep Power
    0

    Re: Daikin Fan Fault

    Thanks Guys,

    Found problem welded relay on PCB

  5. #5
    Join Date
    Dec 2006
    Location
    London & Surrounding Counties
    Posts
    122
    Rep Power
    18

    Re: Daikin Fan Fault

    There were known problems with a batch of Daikin outdoor condensor fan motors, where by the protective seals failed and allowed water ingress causing a dead short, however that tended to blow the PC boards to bits. Glad you found the problem just thought I'd mention this as we're on topic.

Similar Threads

  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  2. Daikin fault codes
    By fridge doctor in forum Air Conditioning
    Replies: 17
    Last Post: 19-09-2007, 10:17 AM
  3. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  4. Daikin VRV Fault
    By licencetochill in forum Air Conditioning
    Replies: 3
    Last Post: 16-06-2007, 08:48 AM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •