    R502 TXV in a R22 system



    What potential problems exist when using a R502 TXV valve in a R22 walk in cooler?
    Can correct superheat be acheived at the compressor and evap outlet?
    Last edited by AzRob; 12-09-2007 at 02:17 AM. Reason: text size too large



  2. #2
    Join Date
    Nov 2006
    Location
    Kettering
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: R502 TXV in a R22 system

    Hi
    You can get away with it but as R502 has a higher working pressure, more problems occur with an external valve, ie flooding back as it will try and achieve higher running pressures. As in reverse if you use a lower running pressure valve, ie R12 it will starve the coil. To be safe always match the TXV to the system. I only ever did it in desperate needs.

  3. #3
    RefTech's Avatar
    RefTech Guest

    Re: R502 TXV in a R22 system

    The system will flood as the pressures obtained with 502 in the bulb will be greater than pressures produced by 22 even with no superheat, so the valve will not close sufficiently to produce superheat

  4. #4
    Join Date
    Sep 2007
    Location
    Casa Grande, Arizona
    Age
    61
    Posts
    19
    Rep Power
    0

    Re: R502 TXV in a R22 system

    It is an external type with bulb placement in the refrigerant stream.
    Given an evap temp range of 20-34 degrees, R502 is about 10 psi higher than R22. Can an adjustable (R502)TXV valve be adjusted to obtain the needed 5-7 degree superheat at the evap? Additionally, the distributor is orficed (to a R22 spec I'm assuming)
    There is a hissing sound in the evap, from which I understand indicates a low charge, but sight glass is now clear. I'm trying to get a good picture of the operating principles for this system.

  5. #5
    Join Date
    Nov 2006
    Location
    Kettering
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: R502 TXV in a R22 system

    As before you can play with it to obtain a running system but as temperature conditions and system pressures change the valve won't response correctly, basicly the buld is charge with r502 to match the system pressures. You really need a R22 valve, expandsion valves can effect systems in alot of ways. ie superheats,discharge pressures and suction pressures. If a the vavle is hissing with a full charge(clear liquid line sight glass) then the vavle needs opening. What evap superheats and pressures are getting?

  6. #6
    Join Date
    Jan 2007
    Location
    Chesterfield, UK
    Posts
    79
    Rep Power
    18

    Re: R502 TXV in a R22 system

    I have done it... and i'm not proud of it, it works in an emergency. Dont use a 134a valve on a R404a systen though, it doesn't work at all.

    Just treat the system to a shiny new R22 valve.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •