Thread: Subcooling on home AC
10-08-2007, 04:42 PM #1
Hello, I am a novice at air conditiong & need some help. Last winter I had a contactor install a larger (4 TR) coil & put in a TXV on my air conditioning system when he changed my furnace out to a high efficiency unit. My condensing unit is a 3 TR York 10 SEER on R-22 that is about 5 years old. My question is what subcooling should I be seing out of it so I can check the charge. I can't find this information anywhere as it appears TXV's are only used on higher SEER systems. If you need data we can assume 85'F ambient, 70# suction and 75'F indoors with about 230# head.
The contractor I used did not know what he was doing and I dont believe his charged the system correctly as he put the sensing bulb for the TXV inside the coils cabinet & attached it with Nylon ties. I corrected this when it got hot and my suction SH dropped from 30'F to 15'F at the compressor and my suction pressure increased about 5 psi. The unit is cooling much better now as you can imagine.
10-08-2007, 09:46 PM #2
Re: Subcooling on home AC
The subcooling is designed for the pressure drop in the refrigerant liquid line to avoid flash gas bubbles in the liquid line fed to the expansion valve. 10°F (5K) is a good value with compressor fully loaded and condenser and cooler fan on full speed. It is important that you measure the liquid refrigerant pressure and temperature at the same point.
10-08-2007, 11:17 PM #3
If the TXV is working correctly then the charge is correct.
Subcooling
By terryw in forum Supermarket RefrigerationReplies: 12Last Post: 07-03-2007, 09:53 AM -
Coil in Coil condensors and subcooling.
By Bernoulli in forum IndustrialReplies: 5Last Post: 16-12-2006, 08:21 AM -
Subcooling & Refrigerants
By US Iceman in forum FundamentalsReplies: 40Last Post: 29-04-2006, 02:59 AM -
Training at Home
By Latte in forum TrainingReplies: 20Last Post: 27-03-2004, 12:38 PM -
Home Generators
By subzero*psia in forum Chit Chat & Service StoriesReplies: 2Last Post: 01-06-2001, 02:00 PM