    toshiba accumilator problems



    good afternoon
    i'm sorry for the spelling, but i'm working at an old toshiba rav 200 uh unit which has a few leaks on the accumilator due to it being on the coast. i've just been to hrp and they are having problems getting me a new one.
    i'm just wondering would it be ok for me to cut it out of the system and re pipe without having any accumilator.
    i look forward to hearing from you soon
    sid



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: toshiba accumilator problems

    Hi Sid

    I'd say no. Could you measure it and get a similar sized one from a component manufacturer such as Henry, Heatcraft, or Esk Schultze (Nrs, Rpw,Dean&Wood) If the original is obselete.

    Jon

  3. #3
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: toshiba accumilator problems

    I'd say no, if its a heat pump, on off cycle defrost liquid will slug the compressor
    fridge

  4. #4
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: toshiba accumilator problems

    u can change with one of same size, i'm shore u cand find one
    and where is the leak , i had one on a sky air - DAIKIN
    and it whas on the welcing's, and there whare a lot, litle, but over 10 leaks , i tuck it out, whent to a company where they wheld inox piping's and they welded for 20 dolars or somth like that a few yars ago, and they weld like profesionals, and cleaned it, pressure test it, and fited back tu the sistem , it whas just like new

  5. #5
    Join Date
    Mar 2007
    Location
    London, UK
    Posts
    36
    Rep Power
    0

    Smile Re: toshiba accumilator problems

    thanks for your help, i will see if i can get may hands on a different make...

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: toshiba accumilator problems

    If you look at any manufacurers split systems technical specification you will normally find that the cooling only model will not have a suction accumulator unless precharged for long pipe run.
    But the same heat pump model will have suction accumulator. This is needed to prevent liquid back to compressor.

  7. #7
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    22

    Re: toshiba accumilator problems

    Hi Sid,

    You'll have trouble finding an accumulater for the RAV-200UH because a) that model doesn't exist and b) 'UH' in Tosh talk is a cassette and accumulators are fitted to outdoor units.

    So I'd guess you either have an RAV-200KH hi-wall system or an RAV-260UH 4-way cassette system.

    Which in turn means you either have an RAV-200AH or an RAV-260AH(8) outdoor unit.

    Use part number 43148116 for the RAv-200AH or 43148114 for the RAV-260AH(8).

    Any Toshiba distributor should be able to check availability and prices.

    Don't run the system without an accumulator the risk is 'liquid carry over' ie compressor trying to pump liquid refrigerant with dire consequenses.

    Hope this helps

    Loops

  8. #8
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    46
    Posts
    54
    Rep Power
    19

    Re: toshiba accumilator problems

    had this problem myself. i just used my angle grinder to take off the rust then i silver soldered over area (the rust had eaten through steel casing causing a pin hole)

    i know its not ideal but it held a 400psi strength test and 270 psi 24hr test and it was ok, it also only meant that unbit was down for 2 days (instead of weeks trying to source parts)

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. Toshiba Warranty
    By gwilliamson in forum Air Conditioning
    Replies: 1
    Last Post: 17-05-2006, 05:59 PM
  3. Toshiba A/C Compressor size
    By Chris2005 in forum Air Conditioning
    Replies: 9
    Last Post: 10-04-2005, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •