Thread: coil temp for r22 split system
-
28-07-2007, 06:03 PM #1
coil temp for r22 split system
what should my evap coil temp be on an 80F 75% humidity day. This is a 5ton goodman split system with a txv. It just doesnt seem to be cooling to capacity. Evap temp is always around 45f. System pressures are HI 250 LO 72, any ideas thanks
-
28-07-2007, 06:23 PM #2
Re: coil temp for r22 split system
Sorry,
Never had the pleasure to work on a Goodman unit.
But the data you provided looks like if it could be OK.
More interesting thou, what's the Delta T (temperature difference across the indoor unit) and superheat?
Those 2 values will tell us more....
-
28-07-2007, 06:55 PM #3
Re: coil temp for r22 split system
Air con is designed to be 20K. So say in celcius, if indoor temp is 20C, saturated suction temp on the LP gauge would be 0C, or ~ 400kpa.
Convert that to moon measurements of PSI and Farenhiet.
eg 30C (85F) day, sst should be 10C = 539kpa or 78 PSI.
-
28-07-2007, 09:36 PM #4
Re: coil temp for r22 split system
then I guess it is running properly, The fact that the unit is for a restaurant that has two large exhaust hoods running all day doesn't help either.
Similar Threads
-
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM