20-03-2003, 12:49 PM #1Geez.
That means about 40ft/12m of 3/8" tubing, with a copper<->water surface area of 3591 cm2 (0.36m2/3.2 sq.ft) and a refrigerant<->copper surface area of 2912 cm2 (0.29 m2 / 2.6 sq.ft).
How much refrigerant->copper->liquid surface area is used with those >20kW chillers you guys are used to work with? Those must be huge....
As I recall, all of the heat flow formulas have electrical flow formula equivalents, with TD representing voltage and heat flow representing amperage, if that helps. In adding surface area, we are lowering resistance.
Gary, I also have another question on which you might have a good opinion. I am using a water/methanol mixture as the secondary coolant. Based on numbers it should perform very well. And in my system if outperforms propylene glycol based automotive coolant hands down.
An ultra low temp liquid chiller is quite unique. Usually the product is chilled directly, but then, this application is unique in that the product to be cooled (CPU) is extremely small.
Using a liquid chiller for this purpose limits the potential, but has it's advantages also.Last edited by Gary; 20-03-2003 at 12:55 PM.
Similar Threads
-
Pressure Transmitter R134a Setpoints
By cooltrain in forum Technical SpeculationsReplies: 0Last Post: 28-02-2005, 09:05 AM -
Is there anything about R134a that is better than R12?
By dude in forum RefrigerantsReplies: 5Last Post: 01-03-2004, 09:59 PM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM -
Minimal required R134a speed in suction line
By DaBit in forum CPU OverclockersReplies: 32Last Post: 08-05-2002, 05:19 AM -
Effect on design evaporator by using R507 instead of R22
By lappee in forum RefrigerantsReplies: 2Last Post: 18-09-2001, 05:15 PM