Thread: Retrofit

  1. #1
    Join Date
    Jun 2006
    Location
    Adelaide
    Posts
    9
    Rep Power
    0

    Retrofit



    I have a system that needs retrofitting. It is currently running on R12 with suniso 3gs oil. If I retrofit with R409A all I need to do is reclaim the old refrigerant and I am going to drain the oil and replace with fresh but that should be it.... Shouldn't it ?

    Do I need a new tx valve ? Or to replace the orifice ?
    Anything else....



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Retrofit

    MP49, No new oil, txv should work well.

  3. #3
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: Retrofit

    I would try using 408a if it is available. I am having a lot of success with that, and according to the lierature there are a lot of pluses.

    better performance, higher oil miscibility, less corrosive...etc

    I have encountered a few systems with 409 and plugged cap tubes. I am thinking it is more corrosive and is dragging all the crap it can into the cap tube.

  4. #4
    Join Date
    Jun 2006
    Location
    Adelaide
    Posts
    9
    Rep Power
    0

    Re: Retrofit

    It is a trane compressor- fairly large system, thanks for the tip on 408A. I don't deal with alot of equipment of this age and the retrofit is something a little foreign to me !

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: Retrofit

    For 409A you change the oil and check the TEV superheat setting. 409A has a Boiling Temperature of - 34 Deg C and a Temp.lide of 8.1 K

  6. #6
    Join Date
    May 2007
    Location
    Uganda
    Age
    52
    Posts
    5
    Rep Power
    0

    Re: Retrofit

    Hi,just do as sledge said but after reclaiming the gas and oil as well. fix every thing back top up oil and charge with the requierd gas.Run the system for about half an hour,stop the machine retrofit again then do the final charge.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Retrofit

    I've been using R413A (R49) in ice builders and car ac also. I think that R409A has R22 in it and so will not be available when R22 is no longer made.

    Cheers Jon

  8. #8
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Retrofit

    Like I said, 10 out of 10 Techs I've listend to talk about MP49 where orgasmic over it. So It seems to be the prefered for R-12 retrofits.

  9. #9
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: Retrofit

    Bitzer has a very good document on retrofit of compressors with various refrigerants. If you visit www.bitzer.de you will and go their documents section you will find the file Report. It is a very good reference document for retrofitting.

  10. #10
    Join Date
    Jul 2007
    Location
    Italy
    Age
    55
    Posts
    18
    Rep Power
    0

    Re: Retrofit

    R134a should work fine but for sure you'll need a different type of oil (ester oil).

    In order to avoid acidity in the system you must have maximum 5% of residual mineral oil left in the system (and isn't easy to check it you must have a specific tool called "refractometer").

    Expansion valve should be OK.

    Good luck.

  11. #11
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Retrofit

    Hi there,

    If you want to retrofit remember not to let R12 out first.
    You need to wash the system from mineral oil. This is done by changing the oil to the synthetic one (which is compatible with the refrigerant used ). If you choose a refrigerant which needs synthetic oil then this is the way :
    1- Evacuate the oil from the crankcase as much as possible.
    2- Add correct synthetic oil in the crankcase.
    3- Run the system for a while.
    4- Change the oil again.
    5- repeat this until the oil contamination is below 1%. Remember synthetic oils have a cleaning and washing capabilities because they have alcohol in them.
    6- When you are sure the oil is clean then you can recover R12 and charge the new refrigerant. Also at this stage you have to change the oil to a new and clean one once more.
    7- According to the capacity of the system check the TEV. For sure change the filter to a correct one.

    Good luck
    Cheers
    Even Einstein Asked Questions

  12. #12
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: Retrofit

    Quote Originally Posted by Sledge View Post
    I would try using 408a if it is available. I am having a lot of success with that, and according to the lierature there are a lot of pluses.

    better performance, higher oil miscibility, less corrosive...etc

    I have encountered a few systems with 409 and plugged cap tubes. I am thinking it is more corrosive and is dragging all the crap it can into the cap tube.
    I am sorry, blame this on weeks of 18 hours days, in a scalding hot bakery, and add a pissed off wife. I am usually not this stupid...I dont think.

    409 is a R12 replacement, and 408 is an R502 replacement.

    I will save my posts for after I get some sleep.

  13. #13
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: Retrofit

    The MG pony, Do you mean MP39(401a)? If you mean what you say, i would like to know some more info on it.
    Cheers

  14. #14
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: Retrofit

    I've been using 426a and have had good results. It is also a HFC.
    Good luck

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Retrofit

    *Slaps head* Ya MP39, I all ways call it 49 for some reason.

  16. #16
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: Retrofit

    Ah, no big deal. If that is the worst thing that happens, your doing very well.

  17. #17
    Join Date
    Jun 2006
    Location
    Adelaide
    Posts
    9
    Rep Power
    0

    Re: Retrofit

    Thanks for all the feedback. I have a few years under my belt but this industry is so varied that I learn something new every day- forums like this and the helpful people willing to share their knowledge really make life much easier.

  18. #18
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Retrofit

    I was doing retrofits to r12 and r500 systems back in the 90s, we never did any less than three oil changes, plus a drier change. We never bothered changing the TX, just checking and setting if neccesary.
    The gases available then are probably different to today though, except for r134a that is.
    We had quite a few crankcase seal failures after charging 134a into a r12 systems for some reason though

  19. #19
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: Retrofit

    R408A is a drop in for R502
    R409A is a drop in for R12
    Both contain R22
    R413a is a very good performing drop in, does not contain R22, but do check & adjust the tev superheat.

Similar Threads

  1. Retrofit
    By environtech in forum Training
    Replies: 2
    Last Post: 16-05-2007, 06:32 AM
  2. PLC control retrofit
    By Triggerman in forum Technical Speculations
    Replies: 6
    Last Post: 28-04-2007, 07:13 AM
  3. Autofrost retrofit
    By dascru in forum Transport
    Replies: 5
    Last Post: 10-04-2007, 11:22 PM
  4. retrofit 502 to 404a (hp-62) lots of fun
    By bernie in forum Commercial
    Replies: 2
    Last Post: 22-06-2001, 03:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •