    Jun 2007
    South Africa
    80
    Post suction accumulator control
    A industrial refrigeration design of mine utilses ammonia, screw compressors, evaporators, thermosyphon oil cooling, PHE and evaporative condersers.
    A ND100mm diameter pipe leads from the liquide receiver to the suction accumulator.
    A modulating liquid level regulator, servo controlled, danfoss PMFL125 was specified as the controlling for liquid injection into the suction accumulator.
    My questions:
    a) Could an electronic expansion valve (possible and AKVA20) of adequate size be utilised instead of the PMFL125?
    b) Would control be better utlising an eletronic expansion valves?
    c) What other forms of control are commonly utilised?
    Kind regards
    Aug 2005
    5,302
    Re: suction accumulator control
    Welcome to the RE forums. It's nice to see another ammonia person on the site.
    I'm not familiar with the two controls you mentioned and would have to investigate them.
    Modulating control for liquid feed to a vessel for level control is the best method I believe as it does a better job of controlling the vessel pressure by reducing the pressure spikes.
    The only two other methods I have seen commonly seen are:
    1. low side float valves
    2. or a solenoid valve controlled by a level switch and a hand expansion valve
    Jun 2007
    South Africa
    80
    This is an excellent forum. (I took a while to figure out how to post a message).
    I am fairly new to industrial refrigeration - less than 2 years and do not have a good feel for the systems yet.
    Thus I thought of geeting feedback of these two valves and experience in field. The main reason for selecting the modulating liquid level regulator (danfoss PMFL125) was to reduce the spikes.
    The only question now remain is - is the AKVA20 better...
    Back to the catalogues for me.
    Aug 2005
    5,302
    Quote Originally Posted by samiam
    Don't give up yet.
    Some of the other ammonia people here may have some good comments!
    Mar 2005
    58
    110
    Hi Samiam,
    I don't know if you know this book:
    http://www.ra.danfoss.com/TechnicalI...LA_version.pdf
    It also gives some examples on LP Liquid Level Regulation. (PMFL, AKVA, solenoid+regulating valve, motorised valve, ...); see page 31 and following.
    There is no clear answer to which is 'the best' way. A lot of this comes down to habbits.
    The valve itself is not the most important, but the combination of it with a mesuring/regulating device is. It's important to get a 'well tuned' combination. And this is possible with several combinations.
    Best regards.
    Aug 2005
    5,302
    Hi BESC5240,
    Thank you for posting the link to the book. This looks very interesting!
    Best regards,
    US Iceman
    Jun 2007
    South Africa
    80
    Thanks for the advice - I relooked at the problem and completed the suction accumulator control including the electronic signal interface with the transmitter, etc. This helped.
    Thanks again for the fedback and the link.
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Last Post: 13-04-2010, 08:58 PM
  3. liquid injection triggered on low suction method
    By liptow in forum Fundamentals
    Last Post: 22-03-2007, 02:37 PM
  4. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  5. Suction temp
    By Temprite in forum Commercial
    Last Post: 30-05-2005, 10:33 AM