Thread: Daikin VRV Fault
-
14-06-2007, 05:27 PM #1
Daikin VRV Fault
Hey guys, I have a Daikin Rsey10gk7w1 outdoor that a previous company changed a condenser fan motor on,iv been called to site to check this out after they got arsed out..
Im getting an E0 fault,im aware this is a safety device fault and have checked continuity thru cn2-cn7.. iv found cn4( which comes from the new fan motor) to be open circut..
Iv linked out cn4 at present so at least it runs..
any daikin lovers out there any ideas..
cheers
justin
-
14-06-2007, 11:54 PM #2
Re: Daikin VRV Fault
HI there, you should have 240v going through the gray wires(overloads) to your fan motors.Had a lot of problems with these fan motors blowing due to water getting in..Would also check HP /LP switches. Happy hunting.
-
15-06-2007, 09:07 PM #3
-
16-06-2007, 08:48 AM #4
Re: Daikin VRV Fault
Maybe they didnt change the ventilator.
Best regards,
Renato