08-06-2007, 06:56 AM #1
Oversized Liquid Recievers?? Problems??
Are there any problems associated with using oversized liquid recievers.
Basically i have pumpdown 15-16kg of charge, thus require about 18kg of pumpdown capacity. However have 28kg liquid reciever.
Is there problems with using oversized liquid reciever?? Will this result in gas being sucked out of liquid reciever back into the cycle thus reducing efficiency of system.
Also what problems are there associated if gas state refrigerant is drawn out of liquid reciever back into the cycle
-
08-06-2007, 07:12 AM #2
Re: Oversized Liquid Recievers?? Problems??
The only problem you will have is that it is more expensive. It can never be tto big but it is many times too small.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
08-06-2007, 12:25 PM #3
-
08-06-2007, 12:30 PM #4
Re: Oversized Liquid Recievers?? Problems??
I agree with the others.
You will not done any harm if the receiver is over sized.
It will have no detrimental effect to the system at all.
If vapour passes out of the reciever then you have other problems, these will not have any bearing to the size of the reciever.
Cheers taz.
-
08-06-2007, 04:32 PM #5
Re: Oversized Liquid Recievers?? Problems??
Originally Posted by nickjhIf all else fails, ask for help.
-
08-06-2007, 06:43 PM #6
Re: Oversized Liquid Recievers?? Problems??
only thing i can think of is it makes for a bigger system that just needs more gas,it will need filling upto the dip tube if its horizontal for the liquid supply, that if it was smaller would take less refrigerant, so as the guys state,better that way than not enough, jump up and down on it a bit to resize it !
-
08-06-2007, 06:46 PM #7
Re: Oversized Liquid Recievers?? Problems??
Well, that's his college question answered for today
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
08-06-2007, 08:14 PM #8
-
08-06-2007, 10:17 PM #9
Re: Oversized Liquid Recievers?? Problems??
We should work out an arrangement with the members for training costs!
If all else fails, ask for help.
-
08-06-2007, 11:22 PM #10
Re: Oversized Liquid Recievers?? Problems??
We're back to to going rate for doughnuts (donuts) I think
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-06-2007, 01:05 AM #11
Re: Oversized Liquid Recievers?? Problems??
Not a college student, but yes im learning on the job.
Adding more refrigerant charge to the system?? could you please elaborate on this, is there any issues of adding extra charge to the sytem. Also the liquid reciever is going to be functioning in a ship enviroment hence the concern about drawing gas in rough seas. Is there any functional issues/concerns if gas is being drawn. There is not room to mount vertically to overcome inclination issues.
-
12-06-2007, 01:15 AM #12
Re: Oversized Liquid Recievers?? Problems??
Shipboard refrigeration systems are a special breed that require some additional considerations. Once of those is what you mentioned about the ship rolling and pitching.
In a standard receiver the diptube (where the liquid comes out of the receiver) is normally cut at a 45° angle and located just above the inside shell radius. Obviously, if the ship rolls the liquid refrigerant follows the angle of the ship.
You may have to use a receiver with an deep enough sump under the diptube to provide sufficient sealing of the diptube. The sump would also have to have sufficient volume to accommodate the refrigerant volume flow at full load during the worse condition.
One of our regular members (Tycho) may be able to offer some additional insight into this problems also.If all else fails, ask for help.
-
12-06-2007, 07:54 AM #13
Re: Oversized Liquid Recievers?? Problems??
the plot thickens !, i dont work on ships but can see the pit falls,i,am not sure a vertical one will be the best solution as you may end up with a reduction in capacity, do they not make one for this application ,horizontal but with a deep diptube and some baffles inside ? that may help in rough seas,
Similar Threads
-
Liquid receiver
By Renato RR in forum FundamentalsReplies: 134Last Post: 02-03-2011, 06:55 AM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Liquid line for multi evaporators
By Kevin Yeo in forum Supermarket RefrigerationReplies: 1Last Post: 29-12-2005, 02:29 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM