    dantoubiana's Avatar
    dantoubiana Guest
    metering device sizing
    what determines the size of metering device needed for a refrigeration system?
    a. the horsepower of the compressor
    b. the Btu capacity of the evaporator
    c. the capcity of the compressor in Btu at the evaporator operating temperature
    d. the capacity of the condenser at the operating ambient temperature
    (please pick one and comment if you'd like)
    Dec 2002
    Malaysia
    59
    86
    22
    The evaporator capacity at the evaporating temperature and the calculated pressure difference between low side and high side , static losses and the friction losses in the pipes and fittings.
    5,667
    I've got to go with (b)
    Frank
    Wouldn't this be better off in a "Poll" format?
    Feb 2001
    63
    264
    Well hopefully you have determined the btu/h requirements for the space and product you are trying to control.... which would give you a specific evaporator rating based on the type of refrigerant you are planning on using... and then the required metering device would be based off that.
    :D
    Dean
    Subzero*psia
    Extinction is simply proof of failure to adapt.
    Feb 2001
    63
    264
    I believe what you are saying here Marc is.... its a "system dependant" question..... hehehehehheh!
    :D
    Dean
    Subzero*psia
    St. Louis, MO
    509
    Amusingly, either b) or c) can be correct, depending upon the situation.
    Given a single evap, single compressor system, sizing based on compressor capacity at the design operating conditions makes sense, and we assume the evaporator is properly sized so that the compressor can operate as design conditions.
    If we have a multiple evaporator system connected to a compressor rack, and perhaps some of the evaporators being controlled with eprs, then one must rely on the evaporator rating at the desired operating condition to size the expansion device.
    Prof Sporlan
    St. Louis, MO
    509
    The compressor(s) shall create the refrigerant flow. And condenser, evaporator, and line sizing shall determine the operating conditions. For metering device sizing, there's the rub....
    Prof Sporlan
    May 2002
    TN
    124
    The rub is: the valve can't pass more ***** than the compressor can pump. If the valve passes less ***** than the compressor wants to pump, operating conditions change to make the compressor pump as much as the valve passes.
  1. Piping and line sizing in lbs/min
    By Kathleen in forum Tools and Calculators
    Last Post: 29-05-2009, 03:07 PM
  2. Compressor sizing using R404a
    By PCL in forum Refrigerants
    Last Post: 14-08-2006, 11:09 PM
  3. Replies: 10
    Last Post: 20-07-2006, 10:00 PM
  4. Sizing for Australia
    By dogma in forum Fundamentals
    Last Post: 17-03-2006, 10:05 AM
  5. Metering device?
    By Apoc in forum Industrial
    Last Post: 20-07-2004, 09:36 AM