Results 1 to 26 of 26
04-05-2007, 12:04 PM #1
Carrier chiller basic board problem
Dear friends I am facing problem on carrier pro dialog plus chiller Model 30GH 025 7290EE this chiller basic board faulty and i replaced with new basic board and removed EPROM from old board. But now display showing "conF" I checked chiller manual they mention when "conF" shows on the user interface this means that the basic board must be configured, this can only be done by carrier service
04-05-2007, 06:48 PM #2
Re: Carrier chiller basic board problem
Hi noushad
Yes,
You have to contact UTS CARRIER, They will up load the new board,
This is the problem with all new chillers processor broads when ever a replacement is required you have to upload it by them.
malik55
05-05-2007, 12:46 PM #3
05-05-2007, 06:35 PM #4
It's okay, Go ahead
Happy to share information if I had, Or may be someone else will help you.
malik55
05-05-2007, 06:55 PM #5
Have you entered the password? Then you can configure the board youself?
06-05-2007, 05:48 PM #6
HI conDor,
The pass word is also a problem,
Pro Dialog chillers usually has 2 pass word , the second one is for the factory set up, and that is not mentioned in any cats,
DO YOU KNOW THAT ONE?
malik55
06-05-2007, 07:22 PM #7
I guess it is Carel board. As far as I understand the eprom has not programmed yet. It has to be programmed by Carrier. Paswords will not help us. Passwords will heplp you after uploading the program to change the parameters.
Best regards
Coskun
07-05-2007, 05:31 PM #8
07-05-2007, 05:39 PM #9
07-05-2007, 06:07 PM #10
Hi Costemur
You are right, the board must first be uploaded and configured, the pass words required for system testing and system setup,
This is for most of the new systems which has micro processor controllers, This is a money making business the manufacturers keeps secrets with them for to make good money, I still remember the old horses, you can at least run the machine by making some alterations, and now if a you don't have a same sensor,transducer, p.c board even a switch the whole system is dead and we feel shame about that we can not fix it.......
malik55
08-05-2007, 02:15 PM #11
Of couse you can program the board (on site), it is a bit tricky, but possible. You will just need the old eprom, the password, and the advanced manual (a few of carriers industrial engineers have it, and know how to do it on site). But you can also use a laptop and a hasp, that is much fastere.
09-05-2007, 03:40 PM #12
When a new board is fitted, it will display Conf. The only way to programme the board is by Carrier Rep using "Carrier Service Tool" with a laptop. In behind the display is a sticker with a code starting with 88CS_ _ _. They will use that code to upload the correct information.
09-05-2007, 06:00 PM #13
It is right that you program the board from the number written inside of the electrical box. The number is identifying what purpose the controller is used for, what refrigerant is used and so on. But it is NOT right, that you can't program it on site without a laptop. Just read the advanced manual, there is a good explanation, on how to do it. But i dont know how hard it is to get, they probably wont give it to everyone. They also have to make a living
09-05-2007, 06:13 PM #14
Hi all
http://www.uk.carrier.com/products/C...n%20ranges.htm
Go to this site find your chiller and download the manual for your controller, it can be done without the laptop it just take great deal of consentration.
we only call in Carrier as a last resort.
Lrac
27-01-2009, 07:36 PM #15
You need to call carrier service an enginer will come out with the correct softwear and upload it.
27-01-2009, 08:05 PM #16
27-01-2009, 09:10 PM #17
TCUK and Moideen.
Did either of you note when these post were added?
IE. 2007
22-08-2009, 07:37 PM #18
hi guys,
i am also facing the same problem with carrier 30gx chiller in my cause compressor scpm board (alarm is loss of comunication with scpm board 3) we tried to replace new board but same alarm comes back does this board also requres software.
22-08-2009, 08:01 PM #19
hi there as said before on this forum no u dont need to configure a compressor board only make sure your dip's are set as previous board and comm is connected ok
good luck
24-08-2009, 10:25 AM #20
The compressor board does need software but this should have been done before you got it. The board has a few different uses and needs the correct software for a screw compressor. Ask your Carrier supplier if the software was programmed onto the board. If it has the software, carry out Goshen advice on checking your connections.
30-08-2009, 05:54 AM #21
hi guys...
i have a pending alarm on my 30gh050 chiller (alarm code 503)...
also i am looking for the manual for the same model...
hope u guys can help me out...
tnx... and more power...
ron
30-08-2009, 06:36 AM #22
hi there hi pressure circuit 5
good luck
30-08-2009, 10:21 AM #23
Ron21 pm me. I'll get you the manual.
01-09-2009, 01:22 PM #24
how old is the plant??? maybe its time to clean the condenser.
Ice
17-06-2010, 06:53 AM #25
Mr.Condor,
can you please describe the steps how to Configure. Thanks
17-06-2010, 06:55 AM #26
Mr.Lrac,
Can you please describe the steps to configure the board and eeproms.
thanks
Carrier Transicold problem
By tsvetomir in forum TransportReplies: 17Last Post: 16-08-2010, 02:59 AM -
Trane HP Defrost Board Problem
By FastEd in forum Heat PumpsReplies: 8Last Post: 05-09-2008, 01:30 AM -
York YK Chiller Problem
By icebox in forum Refrigeration BooksReplies: 13Last Post: 01-07-2008, 06:05 PM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM