    Piping and line sizing in lbs/min
    Hello
    I am looking for a chart that will give me the line sizing from different pressure drop and temperature from the lbs/min of the HFC refrigerant (R-134a, R-404a, R410a). Such as the old ASRHAE RP 185 book and refrigerant line sizing (R-22, R-12, R-502, R717).
    Best wishes for 2003
    kathleen
    Kathleen, P.eng
    www.refri-ozone.com
  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Kathleen, ASHRAE's 2002 Refrigeration Handbook has published line capacities for for R-134a, R-404A, and R-410A (see chapter 2). You may also find Sporlan's Form 5-162 interesting. It lists line capacites for R-134a and R-404A, but not R-410A at the moment. It also contains useful refrigerant data, conversion factors, thermodynamic terms, etc. You local Sporlan rep or wholesaler can get this for you.
    Prof Sporlan
  3. #3
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Hello Prof sporlan,
    In chapter 2 of ASRHAE they give a fast chart but not by lbs/min with different choice of pressure drop, therefore we can decide if it is better to increase or reduce the line sizing.
    I do not have the sporlan one but I will ask for it. Because I would like to review my line sizing for the problem I have with capacity problem. And the chart I use was a fast one in tonnage only, with different line length and I think they might be to short. And a real flow density chart will be of good help.
    best regards
    Kathleen
    Kathleen, P.eng
    www.refri-ozone.com
  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    51
    Posts
    1,630
    Rep Power
    24
    Hi, Kathleen
    I don't use charts, I'am just to lazy to look them up. What I do use is a pipe sizing program from Danfoss called DirCal, this can be downloaded for free from there web site.
    Danfoss Selection Software
    Alternativly they may send it to you by post if you ask nicely.
    If you have any problems on using it it drop me an email, it's very good when you get it figured out.
    Regards. Andy.
  5. #5
    Join Date
    Dec 2006
    Location
    Iran
    Age
    43
    Posts
    55
    Rep Power
    18
    Re: Piping and line sizing in lbs/min
    can i have a copy of this software?
  6. #6
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    I receive my software which works really easy by my danfoss rep.
    Kathleen, P.eng
    www.refri-ozone.com
  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Hi Kathleen,
    Glad to see that you resolved your query here and it's good to see you back with us.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  8. #8
    Join Date
    Jan 2002
    Location
    Canada
    Posts
    35
    Rep Power
    0
    Hi Brian
    be sure refrigeration is my passion, I am always a email closed
    Kathleen, P.eng
    www.refri-ozone.com
  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31
    Hi, Jahangir
    Quote Originally Posted by Jahangir View Post
    Of, course
    follow this link:
    http://www.danfoss.com/United_Kingdo...tion+Tools.htm
    register and download what you need.
    CoolCat, ForeseeT, CoolSelector, RS+3, DIRCalc or DanCap™ 1.0
    or this one:
    http://www.danfoss.com/United_Kingdo...ters+Notes.htm
    Very good fitters notes
    Best regards, Josip
    It's impossible to make anything foolproof because fools are so ingenious...
    Don't ever underestimate the power of stupid people when they are in large groups.
    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.
  10. #10
    fmchadyai's Avatar
    fmchadyai Guest
    Page5 to Page7
    Attached Files Attached Files
  11. #11
    fmchadyai's Avatar
    fmchadyai Guest
    Page8 to Page9
  12. #12
    fmchadyai's Avatar
    fmchadyai Guest
    Page11 to Page15
  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31
    Hi, all
    Quote Originally Posted by Josip View Post
    Hi, Jahangir
    Of, course
    follow this link:
    or this one:
    Best regards, Josip
    Sorry, above link is to an old Version of DirCalc113
    Here is new Version DirCalc114
    http://www.danfoss.com/NR/rdonlyres/...DirCalc114.zip
    also for other software:
    http://www.danfoss.com/Pacific/Busin...tion+Tools.htm
    Best regards, Josip
  14. #14
    Join Date
    Oct 2007
    Location
    MANILA
    Posts
    7
    Rep Power
    0
    hello there
    How can i eliminate condensation in the ducting system. The ducting was locted near the kitchen it was insulated with 1" thick rubber insulation
  15. #15
    Join Date
    Mar 2007
    Location
    USA
    Age
    48
    Posts
    5
    Rep Power
    0
    Smile Re: how to make a custom evaporator
    I want to make a custom evaporator or barrel that works like a chiller I have a condensing unit of 30,000 BTU. with refrigerant 22, i need ideas for the calculation or how to do it.
  16. #16
    Robertoroli's Avatar
    Robertoroli Guest
    Re: Piping and line sizing for ammonia
    Hi to all,
    Anyone have the tables for sizing ammonia piping? I dont have the ASHRAE or IIAR handbook. So if somebody can pass me this information i will be very thankful
  17. #17
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31
    Hi, Robertoroli
    Quote Originally Posted by Robertoroli View Post
    Hi to all,
    Please check the links in above post #13...there you have everything...
    Best regards, Josip
  18. #18
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0
    thanks buddy it is realy useful to me
  19. #19
    lode janssens's Avatar
    lode janssens Guest
    Katleen,
    Go to R717.com and apply for the Free Ammonia Refrigeration Piping Calculator.
Similar Threads
  1. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Last Post: 04-08-2005, 03:46 PM
  2. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Last Post: 08-05-2002, 05:19 AM
  3. Line Sizing and Piping Practice
    By subzero*psia in forum Commercial
    Last Post: 22-06-2001, 03:47 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts