14-04-2007, 10:41 PM #1
noisy working
hı everybody
outdoor unit is working too noisy,
there is hıgh vibration on 4 way valve pipes,especially on suction pipe,ıt ıs causing vibration on outdoor unıt body what can ı do?
please share your experiences with me.
-
14-04-2007, 11:42 PM #2
Re: noisy working
What make/model unit is it ?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-04-2007, 12:10 AM #3
Re: noisy working
24 btu ac and working hitachi comp.
-
15-04-2007, 07:19 AM #4
Re: noisy working
Have you checked the fan. I've had out of balance fan blades caused by a build up of dirt.
Remove fan blade and check the back of the center hub area for accumulated dirt.
-
16-04-2007, 11:55 AM #5
Re: noisy working
thanks,
but fan is normal
-
16-04-2007, 12:41 PM #6
Re: noisy working
Check 4 lock pads .
Or compressor vibrating eliminators....might be demolished.
-
16-04-2007, 01:55 PM #7
-
16-04-2007, 02:14 PM #8
Re: noisy working
I have just seen that Patrick Kotza in his book "REFREPAIR MANUAL", describes a situation that seems to be what you have.
If the slide on the 4-way valve sticks in some intermediate position, all 4 ports will be connected. This effectively short circuits the HP/LP, creating an unstable situation.
The vibration is the slide valve.
-
16-04-2007, 09:06 PM #9
Re: noisy working
I think ıt is concerned with pipe design,I have used 5/8" pipe and I will try 1/2" now.
ı will come back with concluisons