Ammonia evaporative condenser surface
Dear Friends:
Does some body knows the surface area required per MBH at manufacturer std. conditions for a evaporative condenser.
Best regards
Gonzalo ARIAS
-
17-04-2007, 02:25 AM #2
Re: Ammonia evaporative condenser surface
It depends on the manufacturing. It is usually from 2kw/m2 ~4kw/m2 . Only for your ref. You can refer to the specific catalogue for it.
regards
LCI hear...I forget;I see...I remember;I do...I understand
-
18-04-2007, 05:58 AM #3
Re: Ammonia evaporative condenser surface
Thanks LC
I think that Vilter, Baltimore, Evapco have about the same surface area, Do you Know this figures? also Kw/m2 that you stated are evaporator KW or total heat rejection KW?
Best Regards
Gonzalo
-
19-04-2007, 02:20 AM #4
Re: Ammonia evaporative condenser surface
The ammonia evaporative condenser total heat rejection:2~3.3KW/M2 usually;we made copper tube evap condenser and the heat reject is at the upper level.
Hope it can do some help for you. You'll design it or manufacture it?
regards
LCI hear...I forget;I see...I remember;I do...I understand
-
20-04-2007, 06:58 PM #5
Re: Ammonia evaporative condenser surface
TK, this will help, we use carbon steel pipe.