    modifying a commercial reachin



    hey,

    i have a true t49 reachin freezer that currently maintains -10f...im looking to drop it down to -20 using a digital thermostat...just wanna hear what the experts say... will this thing handle the extra workload? we'll keep the doors closed most of the time...only opening it no more than 3 times every 8 hours...and only for a very brief moment to slide a tray in or out...whaddya think?



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: modifying a commercial reachin

    Yes, I don't really see why not.

    It's not that much colder, although you may have to defrost it more often.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: modifying a commercial reachin

    hey,
    I don't think it is a real big deal to run that much colder, but you may want to check with true to see if the compressor can handle running at a lower suction pressure. This may be more critical if the freezer is in a warm location, compression ratio might be out of wack.
    good luck