    hi everyone
    was just wanting to know, i have a daikin split that keeps going out on hp after a few hours of running, the filter is clean, the coils are clean and the fans are running. i suspect a blockage some where, but if this was the cease would it not go straight out on hp..
    Feb 2007
    2,473
    Re: dankin split
    Non condensables?
    Moisture?
    If you pump it down, will it pump down or does it cut out on HP?
    Is it HP or discharge temperature?
    Sep 2005
    Singapore
    145
    Re: dankin split
    What is the operating high, low pressure and running amperes of the compressor? Model of fan coil and condensing unit.
    On coil and off coil air temperature etc.
    Jan 2003
    East Anglia
    1,160
    Re: dankin split
    Does Sound like moisure, do you know the history of the unit. Personally i would start by reclaiming, vac out and regas to weight, If there is a blockage in the condensing unit you mat see one of the pipes iceing up. Poss someones fitted a strainer in the AHU but have only seen this on a mitsi.
    Post the unit details and we may be able to help more
    raymond
    Mar 2007
    London, UK
    Re: dankin split
    Thanks very much for all this!
    I will get details tom and post tom pm.
    Sid
    Mar 2007
    London, UK
    Re: dankin split
    thanks everybody, turns out it was over charged by 2.3 kg of 407c.. dont ask me how this happened but it must have been a cowboy at it before me