    Distributor



    We are executing a Cold Room project. One of my technicians has misplaced the nozzle of one distributor and has connected the TEV. Could some one tell me that in case the the nozzle of the distributor is not provided, what effect would it have on the operation and the performance of he plant.

    At this stage to import the nozzle from the coil manufacturer is going to be time consuming and we have to commission the plant.

    Please advise.



  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Distributor

    The position of the TEV and the quantity of tubes feeding the evaporator would matter. If the valve was feeding in an upright position, you might have some reasonable distribution. If the valve feeds horizontally, there will be a tendency to flood the lower circuits and starve the upper circuits.

    I have seen supermarket cases operate surprisingly well without the orifice in the distributor. But these are coils with only 3 circuits and the accidental luck of feeding in an upright position.

  3. #3
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Distributor

    Hi Samarjit Sen

    It might be worth checking the paperwork that came with the coil, some coils don't need the restrictor depending on what refrigerant your using. Take Frigobohn they always supply a restrictor but you only use it if using R22.

    Kind regards
    Lrac

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: Distributor

    Thanks for the information. The Evaporators being used are from Heatcraft Larkin. I am happy to say that the nozzle has been located and installed. However during this short period I found out that it is important to have the nozzle of the distributor as it balances the flow of liquid and the vapour.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Distributor

    Quote Originally Posted by Samarjit Sen
    However during this short period I found out that it is important to have the nozzle of the distributor as it balances the flow of liquid and the vapour.
    Exactly right. The pressure drop across the distributor is important, and the orifice plays a major role in this.

    In the selection process for the TXV you have the following pressure drops which have to be accounted for to ensure good valve performance:

    1. Pressure drop across the TXV
    2. Pressure drop across the distributor (with the proper orifice)
    3. Pressure drop across the distributor tubes
    All three of these are used.
    If all else fails, ask for help.


  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    51
    Posts
    1,630
    Rep Power
    24

    Re: Distributor

    Quote Originally Posted by Samarjit Sen View Post
    Thanks for the information. The Evaporators being used are from Heatcraft Larkin. I am happy to say that the nozzle has been located and installed. However during this short period I found out that it is important to have the nozzle of the distributor as it balances the flow of liquid and the vapour.

    Heatcraft and Frigobohn are one and the same

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes: