22-08-2002, 01:03 AM #1
r-23 low stage, cascade system
Hello out there. I am working on a cascade system with r-23 for the low stage and r-22 for the high stage. I'm trying to recover the low stage with a high pressure recovery unit. It seems it's taking for ever to recover the refrigerent. I got 30 lbs of vapor out in 8 hours? Is there a better way?
-
22-08-2002, 03:52 PM #2
Your recovery system is not designed for that job. After you get the liquid out of the system, put a vacuum pump between the system and the recovery machine. You can get a fitting to screw into the outlet of your vacuum pump. This increases the pressure on your recovery compressor and decreases the dicharge pressure on your vacuum pump.
P.S. I have an old vacuum pump that I pipe in parralel with a good pump to draw deeper vacuums quicker as well.
-
06-08-2007, 09:53 PM #3
Re: r-23 low stage, cascade system
I know this is an ancient post but thought id share my view. I just stick the recovery cylinder in another chamber if available amd take it down to -60 before starting the recovery.
-
16-08-2007, 04:59 AM #4
Re: r-23 low stage, cascade system
I accually do use the overpriced EPA appoved high pressure refrigerants recovery machine. But then I charge for its use.
The only mechanical one on the market is listed a 1/2 pound vapor per min.
Basicly you just have to put the machine on... go do another call or two.Will melt ice for $101/hr
-
09-09-2007, 08:29 PM #5
Re: r-23 low stage, cascade system
Johnny, Have the same problems here in holland. Same system. have tryed placeng a recycle cil. in a large container with cold-ice. If temp goes down it makes it a little easier. but there's no way to get it all in a cilinder.
ps. Wach out when such a system goes up in temp. Pressure of the R23 will be 30 bars or more when temp comes above 10 degrees.
Good luck
-
29-03-2009, 01:50 PM #6
Re: r-23 low stage, cascade system
I built a recovery unit that uses a high pressure bottle as a condenser. The bottle is cooled with a R507 system. The R507 coils wrap around the outside of the R23 bottle. When the bottle is full I heat it up with anti frost heater cable and let it flood into another R23 recovery bottle. Then I can start again and cool down the first bottle and recover some more R23.
-
05-06-2009, 08:10 AM #7
Re: r-23 low stage, cascade system
Hi
I am trying to design a R23-R22 cascade system. I have decided to have a 5HP scroll Comp for low cycle and 10HP comp for high cycle and a Plate cascade heat exchanger and air cooled condensor. My cooling load is at most 5KW and operating temperatures are -70C for evaporating and 35C for condensing.
I have to have a tight temperature control +/-1C.
I wanted to know if it is ok?!
I don`t have enough catalogues for selecting my compressor, Plate HE, TEV, Solenoid valves,...
whould you please help me?
-
08-06-2009, 02:52 AM #8
-
21-11-2009, 09:01 PM #9
Re: r-23 low stage, cascade system
i still deal with r-13 as well as r-23 , if you have liquid nitrogen and a portable j/c with a solenoid valve you can make a coffin insulate it an pump that into that with the container inside usual go to -130 that's 0 psi for 13. use that about once a month. never had a problem. open up the low side the refrigerant just walks out the compressor into the bottle.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Cascade Refrigeration System
By Vincent Yu in forum FundamentalsReplies: 71Last Post: 16-02-2012, 04:04 AM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
R-23 cascade system
By S.M.Gokhale in forum IndustrialReplies: 22Last Post: 08-08-2009, 08:04 AM -
problem in Auto Refrigeration Cascade System
By ernestlin in forum Trouble ShootingReplies: 17Last Post: 01-07-2009, 12:41 PM