Thread: chilled water PHE
Threaded View
-
31-07-2002, 08:25 PM #2
Hi, Priti,
Just I few quick sugestions.
1/Refrigerant charge
2/Expansion valve/level control problem
3/Reduced water flow due to dirt blocking a pump strainer
4/Damaged pumped.
I would try to establish pump flow rates on the Glycol/Brine side. If you have a flow meter on your system this is very simple, otherwise you are depending on commisioning data, such as temps in and out of the chiller and pump Amperes.
Regards. Andy.