Results 1 to 10 of 10
    gspatch's Avatar
    gspatch Guest
    FX56 Drop in gas
    Anybody used FX56 made by Elf Atochem ?
    If so how did it perform and were there any changes required
    besides new drier.
    Any comments
    Jun 2001
    N.Ireland
    1,630
    gspatch,
    What is the R400 number for this refrigerant? Having said that most of these drop-in mixes actually improve system performance, with usually a smaller charge.
    Regards. Andy.
    Apr 2001
    79
    5,071
    35
    FX56 is R409A.
    Jan 2002
    Austin, Texas
    716
    I use 409A regularly. Pressures are higher. I do not use it in any medium temp Tecumseh equipment, because they admit that they do not have enough condenser coil to operate with 409A in Central Texas summer conditions (ambients up to 110degF).
    I check max evap temp of equipment that I am going to utilize a replacement (for r-12) carefully, and if the unit too near the max at design, I will use 416A (in med. temp only). In a low temp (R-12) application, I have had no problems at all (even in Tecumseh equipment). However, I find any low-temp R-12 to be pretty rare anymore.
    Jun 2001
    N.Ireland
    1,630
    I tend to use 401a instead, this has a slightly higher head pressure compared with that of R12, due to the UK ambients I have not had any cases where a cmpressor burn-out has occured due to the gas change. On the other hand I fitted R409a to friends bulk milk tank and the condenser gave up the next summer.
    Regards. Andy.
    May 2002
    TN
    124
    I predict that most new restuarant equipment will be using 404 in a couple of years. It is the only true low temp ***** out there. I am seeing alot more 404 medium temp systems. I have not seen any 507 systems, why is that ***** on my gages?
    May 2001
    West Lafayette, Indiana, US
    FX-56 (R409A)
    FX-56, in addition to "too much R22",
    and hence higher head pressures,
    also may have mineral oil return problems
    below 32F. Below 32F, mineral oil
    (150 SUS), goes "two phase", and may or may
    not return, depending on equipment geometry
    and line velocities.
    Two R-12 replacements that I invented,
    R-406A, and R-414A, have mineral oil two
    phase points of around -40F and -10F and lower
    head pressures than FX-56. One could also
    use Alkylbenzene oil to get good oil return
    since it's two phase points are much lower
    than regular mineral oil. Whirlpool distributes
    R-414A in the US, but I doubt if either
    R406A or R414A is avail in Europe.
    Atofina (formly Atochem), who invented FX-56,
    according to the grapevine, has submitted
    a new HFC blend, Dimethyl Ether, R125/R134a
    to ASHRAE for an R-number. While it may be
    weakly flammable, it should make an excellent
    R12 replacment as well.
    --ghg, www.autofrost.com
    St. Louis, MO
    509
    Atofina (formly Atochem), who invented FX-56, according to the grapevine, has submitted a new HFC blend, Dimethyl Ether, R125/R134a
    Curious why one would use dimethyl ether, a somewhat expensive gas, as opposed to a less expensive propane or butane series gas. Or is the Prof confused with gas costs?
    Prof Sporlan
    May 2001
    DME for the prof.
    Dupont makes it is "propellant", and also
    several research projects underway to use
    DME as a cleaner burning substitute for
    diesel fuel..
    It appears to just be expensive, when
    purchased from specialty gas suppliers..
    DME has excellent affinity for mineral oil,
    and dissolves in it well (GHG-X6 used DME).
    Also, boiling point of DME is about -11F,
    which is close to R134a at -14.7F.. so the
    R134a will inert much of the DME's
    flammability. Nearby "cheap" hydrocarbons are
    isobutane, with BP of +10F, and propane
    with BP of -44F. Neither is close to the
    BP of R134a.
    --ghg
    ps. How do your dry-eyes (See-Alls) and
    Driers work with DME? CH3-O-CH3 ?
    St. Louis, MO
    509
    How do your dry-eyes (See-Alls) and Driers work with DME? CH3-O-CH3 ?
    See-All change points and filter-drier water capacity will depend upon the refrigerant's water solubility. If DME has a water solubility similar to one of the standard refrigerants, you can generally be safe with change point and water capacity data for that refrigerant.
    Prof Sporlan
  1. A question about the pressure drop in coil .
    By jackcn in forum Fundamentals
    Last Post: 13-12-2008, 05:10 PM
  2. pressure drop of pump return line ammonia