surely not
Surely yes...

In fact, warming the sensing bulb up may not help much if it happens to be an MOP (maximum operating pressure) type charge. By definition, these types of thermostatic charges close off the TEV above a certain suction pressure.

Low side pressure is a closing force on a TEV. The higher the low side pressure, the more you force the TEV in a closed direction.