    ireland
    1,451
    Toshiba VRF systems
    Hi gang
    is anyone familiar with these systems? am wondering is there a minumum distance that the flow control boxes should be apart? have an install where i can place boxes is 1m proximity to each other due to lack of ceiling space. also can the refnet joints be placed vertically?
    Al
    Jun 2001
    N.Ireland
    1,630
    Re: Toshiba VRF systems
    Quote Originally Posted by al
    Hi gang
    Al
    One word Al NOISE
    The BS boxes are usually placed away from the unit to kepthe noise out of the occupied space, just watch that there is not too much carry over of that noise to any area you don't want
    Kind Regards Andy
    5,667
    I've got photo that might answer your question. I think it's on the work computer. I'll have a look tomorrow.
    NO, no, no, Refnet joints should be horizontal or the branch slighty below the main to ensure even flow of refrigerant.
    ireland
    1,451
    Thanks guys
    noise could be an issue, but there's no other space available.....the install instructions state that vertical is ok but i know with daikin this isn't so....are tosh that good
    regards
    al
    May 2006
    Hayling Island, UK
    143
    22
    Hi Al,
    I'm very familiar with these systems in fact we are having both a 3-pipe and a 2-pipe Tosh VRF installed in our offices.
    The header type refnet should be kept within 10° of the horizontal.
    The Y type refnets can be either verticle or horizontal - although if horizontal then within 15°.
    See page 21 of the 'SHRM' (3-pipe) installation manual A04-002.
    Noise is not a problem with these BS boxes and they can be installed close to the indoor unit. They are well insulated internally.
    Standard is a 5m limit between BS box and the indoor unit, although there is an extension accessory to take this up to 15m.
    Also worth noting that there is spec calling for a 500mm straight pipe into the BS box. To reduce turbulance and noise I guess.
    So the answer to your question would be minimum 1000mm between boxes - with a refnet half way between the pair of them that is.
    The BS boxes must be kept up-right for correct flow through the PMVs.
    Loops
    ireland
    1,451
    loops
    Thanks very much for that.
    al
  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Last Post: 18-10-2010, 02:45 PM
  2. My local Apprentice Training Classes
    By shogun7 in forum Training
    Last Post: 17-03-2007, 03:10 PM
  3. Toshiba VRF systems
    By puddleboy3 in forum Air Conditioning
    Last Post: 01-08-2006, 09:28 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Last Post: 21-04-2006, 10:02 PM