    fix_it_man74's Avatar
    fix_it_man74 Guest
    glass display case compressor on, off, on, off......
    I am working on an old refrigerated glass case, when I powered it up it imeadiately kicked the breaker in the breaker box, arced and smoked. I replaced the condenser fan motor, now the unit will power up and the compressor will run for a 20 to 30 seconds then shut down, then on again and shut down. All other components seem to be working properly, and the sight glass seems to read sufficient refrigerant. Thanks for any help.
    May 2006
    china
    98
    Re: I may be spittin in the wind, but...
    Hi, It's may be protected by high/low pressure protector, suggest you check the high/low pressure.
    Jul 2006
    Romania
    44
    99
    hy ! you can check also the relay start of the compressor ar the capacitor..
    Jun 2001
    N.Ireland
    1,630
    Re: glass display case compressor on, off, on, off......
    Quote Originally Posted by fix_it_man74
    Hi fix it
    the compressor bimetal klixon for over current, could it possibly be cutting out
    Using a clamp meter I would check the compressor run amps
    Kind Regards Andy
  1. Part Wind/ Star Delta
    By reggie in forum Technical Speculations
    Last Post: 27-08-2008, 05:47 AM