25-07-2006, 12:20 AM #1
expansion valve aint cold
Hi all
I have an old R22 that i am fooling aorund with. I installed an expansion valve and it isnt cold. The evap coil is cold and the tube into the compressor is cold but the expansion valve isnt cold. The tube connecting the expansion valve to the evap is not cold also.
What is the problem
thanks
-
25-07-2006, 05:05 PM #2
Re: expansion valve aint cold
Hi Justin and welcome to RE.
What sort of 'cold' are you looking for?
Some pressure/temperature readings would help with the analysis.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-07-2006, 02:51 AM #3
Re: expansion valve aint cold
maybe i did not make my problem clear
first off i dont have any pressure reading, just temp after the compressor outlet,
here is the problem
The pipe after the expanion is not COLD. The pipe into the evap is cold and the evap is cold, as well as the pipe into the compressor. In additon the pipe into the compressor is sweating
the pipe after the expansion valve but before the evap is not cold but is is luke warm and and alot cooler that the pipe after the condenser
any reason for this, i thought the pipe after the expansion valve would be cold not luke warm
do u think i am overcharged, i am not using a receiver
-
26-07-2006, 03:23 AM #4
Re: expansion valve aint cold
If I might ask a question or two;
Why don't you have pressure readings?
How do you expect to find the problems then?
Seriously now, you are asking us to guess along with you with no more information than what you are offering.
Obviously you must have a set of gauges, since you asked about the possibility of overcharging. If you don't have a set of pressure gauges and are charging refrigerant, stop before you hurt yourself.
You can't use a TXV without a receiver without the risk of misinterpreting the system charge.
Do you have any training to be doing this?
-
26-07-2006, 03:27 AM #5
Re: expansion valve aint cold
i am not using a txv, i am using a manual expansion valve, that i can adjust as i please.
this is is a small 1kw system, an old a/c system that i am fooling aorund.
-
26-07-2006, 09:45 PM #6
Re: expansion valve aint cold
Originally Posted by justinworne
-
26-07-2006, 10:52 PM #7
Re: expansion valve aint cold
Originally Posted by frankBrian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
Thermostaic expansion valve for NH3 refrigeration system.
By hphien in forum NH3Replies: 17Last Post: 04-12-2005, 09:06 PM -
I want to find detailed files about ALCO zz thermo expansion valve
By brightfu1 in forum FundamentalsReplies: 2Last Post: 07-09-2005, 03:07 PM -
pressure drop between expansion valve and distributor
By aygul in forum Technical SpeculationsReplies: 10Last Post: 22-01-2004, 09:47 AM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM