Thread: TXV icing but room warming
-
28-06-2006, 02:07 PM #1
TXV icing but room warming
Hello cool people,
First time post for me.
If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?
I just figure it is low on refrigerant but could somethin be wrong with the design?
We're talkin 2HP Copeland w/ r134a for a 4c room.
TXV is Alco with MOP thermal bulb charge.
Thanks folks, Joe.
-
28-06-2006, 04:14 PM #2
Re: TXV icing but room warming
1) Low on gas. Check SH, SC and eventually fill it up.
2) Liquid solenoid blocked. Change diaphragm.
3) Liquid filter clogged. Replace core.
-
28-06-2006, 06:37 PM #3
Re: TXV icing but room warming
Originally Posted by NoNickName
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes:
-
28-06-2006, 07:27 PM #4
Re: TXV icing but room warming
Strainer on inlet of TXV partially plugged
-
28-06-2006, 07:29 PM #5
Re: TXV icing but room warming
If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?
-
28-06-2006, 08:01 PM #6
Re: TXV icing but room warming
Thanks all.
And Frank, can I be in your foursome?
Joe
-
28-06-2006, 08:16 PM #7
Re: TXV icing but room warming
Originally Posted by liptow
-
28-06-2006, 08:26 PM #8
Re: TXV icing but room warming
What's a 4c room? I personally like more a 5 W room
Pressures readings?
Temeprature readings SH and SC?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
30-06-2006, 09:01 AM #9
Re: TXV icing but room warming
I play golf, do I qualify?
Similar Threads
-
troubleshoot a two door storage room
By duraid in forum FundamentalsReplies: 7Last Post: 13-12-2006, 06:57 AM -
Cheese Room Design 24V DC
By jbelding in forum FundamentalsReplies: 10Last Post: 02-04-2006, 03:23 PM -
Installation of cold room
By Josip in forum Legal-Business-MarketingReplies: 12Last Post: 12-03-2006, 09:20 PM -
Freezer Room Panels
By Feeze in forum Technical DiscussionsReplies: 10Last Post: 22-04-2005, 05:58 AM