16-06-2006, 02:58 AM #1
Overload tripped lesson
Hi
What are the causes of this overload tripped?
thanks, rosliin.
-
16-06-2006, 07:09 AM #2
Re: Overload tripped lesson
overload relay trips due to eccessive load than the rated load i.e motor consuming current(over load relay which converts heat energy into mechanical force)
-
16-06-2006, 11:40 AM #3
Re: Overload tripped lesson
which overload?
-
16-06-2006, 12:14 PM #4
Re: Overload tripped lesson
Hello
are you ensure your setting is correct? if it is ok ,
pls check your voltage in the range. or your have a high ambient temperature .
hope it is helpful to you
Best Regards
Neil
-
19-06-2006, 03:55 AM #5
Re: Overload tripped lesson
olp tripped.
why eccessive load can be happened?
-
23-06-2006, 12:33 AM #6
Re: Overload tripped lesson
i find the usual causes of overload tripping are,compressor burnt/siezed, system blocked.
CHILL out with Manchester United
-
23-06-2006, 11:29 PM #7
Re: Overload tripped lesson
Originally Posted by rosliinBrian - Newton Abbot, Devon, UK
Retired March 2015
-
24-06-2006, 12:13 AM #8
Re: Overload tripped lesson
Some causes of overload trips of compressors are:
1. Refrigerant floodback;
2. Flooded starts;
3. Slugging;
4. Overheating; and
5. Loss of oil.
-
26-06-2006, 03:49 AM #9
Re: Overload tripped lesson
Ooh, i'm ac trainee technician.....
but thanks.