Thread: Mitsi Fault
-
14-06-2006, 07:32 PM #1
Mitsi Fault
Hi,
Breify looked at system not cooling today, its a twin split with a PUH-5... outdoor on R22.
The filters on the 2 cassettes were blocked so washed them out but was getting a P8 (abnormal discharge temp?) fault on the remote.
Put my gauges on the suction schreader, had a head pressure of around 7.5bar, and ran the sytem in test mode. Compressor ran, air off condenser was just ambient, liquid line was sweating, suction was around 1.5 bar. So first thoughts were that it was undercharged. On closing of manifold gauge after adding some vapour, the pressure remained at around 7.5bar again, with the comp still running.
Could there be a blockage somewhere? The suction service valve is after the 4-way reversing valve if that helps?
-
14-06-2006, 07:41 PM #2
Re: Mitsi Fault
Hi slim
we have had reversing valves stick half giving the fault you have idicated,i suggest you switch the unit off a lightly tap the body of the valve or energise the coil a couple of times to see if it seats properly.
-
14-06-2006, 09:06 PM #3
Re: Mitsi Fault
Thanks for the help,
I tried tapping the valve whilst it was running but not while it wasnt. When you say energise the coil I presume you mean ask it to heat, should there be 240v on the coil when it asks for heat mode?
-
14-06-2006, 09:24 PM #4
Re: Mitsi Fault
Originally Posted by Slim R410a
-
15-06-2006, 01:31 PM #5
Re: Mitsi Fault
Originally Posted by Slim R410a
Similar Threads
-
Chiller fault
By iceman007 in forum Trouble ShootingReplies: 9Last Post: 27-06-2006, 06:15 AM -
Chiller Fault
By iceman007 in forum Air ConditioningReplies: 2Last Post: 13-05-2006, 07:23 PM -
Mitsi Fault
By richelli in forum Trouble ShootingReplies: 2Last Post: 27-03-2006, 07:20 PM -
Mitsi HEAVY
By Latte in forum Air ConditioningReplies: 4Last Post: 27-01-2006, 02:21 PM -
Mitsi Problems
By Latte in forum Air ConditioningReplies: 9Last Post: 12-02-2005, 07:22 PM