10-05-2006, 12:43 PM #1
cooling tower & humidity
dear all
i know that cooling towers do not be efficient on humid atmosphere ,,,,but what is the maximum relative humidity we can allow to install cooling tower?
thanks
-
10-05-2006, 02:27 PM #2
Re: cooling tower & humidity
afeef,
The cooling tower capacity quickly reduces as the entering air wet bulb temperature increases. If the entering air relative humidity is 100% then the wet bulb temperature is the same as the dry bulb temperature, so the capacity would be almost zero.
You can derate the tower capacity for higher entering air wet bulb temperatures but this has the effect of increasing the tower cost and size.
When the wet bulb temperature begins to reach 80F (26.6C) the tower sizes, costs, and capacities change very quickly.
-
10-05-2006, 07:40 PM #3
Re: cooling tower & humidity
afeef,
Here is some additional information that may be helpful to you.
http://www.marleyct.com/catlinks/CTII-1.pdf (168 kb)
There are lot of good technical topics on water cooling towers also at:
http://www.marleyct.com/publications.asp
-
11-05-2006, 05:28 AM #4
Re: cooling tower & humidity
thanks us iceman
god bless you
-
11-05-2006, 02:41 PM #5
Re: cooling tower & humidity
Glad to help afeef. I hope the information is useful.
Similar Threads
-
Cooling Tower Design
By jteixiera in forum Tools and CalculatorsReplies: 10Last Post: 31-01-2006, 12:23 AM -
cooling tower without fillings
By Lc_shi in forum FundamentalsReplies: 3Last Post: 27-12-2005, 12:55 AM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum IndustrialReplies: 5Last Post: 14-10-2005, 06:34 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum FundamentalsReplies: 0Last Post: 13-10-2005, 05:14 AM -
Cooling tower water pumps
By reggie in forum FundamentalsReplies: 1Last Post: 13-08-2003, 08:18 PM