    Hi every body,
    I've read in many articles that the RH % in a potato cold sotrage should be never less than 90, and there is many equipment manufacturers assuring to reach that percentage.
    My question on this is related to an aplication with potatos storaged in wood boxes, the highest RH at the Higrometer location is no more than 80%, there is three evaporative coolers inside and the amount of water condensed at the cooling coils is below the amount of water consumed by the evaporative coolers.
    I think I'm missing something.
    I'm looking for help.
    Croatia
    68
    2,261
    Re: RH in potato cold storage
    Quote Originally Posted by kryoboss
    Hi every body,
    Hello Kryoboss,
    Please check something more at this link:
    http://www.uidaho.edu/ag/plantdisease/potato.htm
    hope to find something useful,
    Best regrds,
    Josip
    May 2006
    India
    82
    1,013
    Hi, Josip,
    In Agricultural refrigeration it is not possible to attain RH above 70 to 80 % from the evaporator coils. There are manufacturers who claim so, but if you study the details the coils can attain 80 to 98& RH if the intake of air to the coil has RH of about 80%. The only way one can attain the RH above 80% upto 98% is by using additional adiabatic humidifiers. Care should be taken that as for other products the particle sizes of moisture is between 3 to 5 microns other wise there shall be droplets of water.
    Air is another important factor. The required quantity of air as per load assessment and product details should be provided at a high velocity to ensure proper circulation of temperature and humidity.
    With best wishes, Samarjit
    Jun 2001
    N.Ireland
    1,630
    Hi every body,
    Hi Kryoboss
    have you a water meter on bthe evaporative cooler water make up, and a bucket on the overflow
    this will tell you if water is being added to the room
    Have you refrigeration checked over, the evaporation may be too low or the plant short of refrigerant.
    Kind Regards Andy
  1. Onion and potato ammonia cold store
    By Josip in forum Industrial
    Last Post: 13-09-2010, 11:39 AM
  2. Cold storage - Onions room
    By Kevin Yeo in forum Fundamentals
    Last Post: 14-02-2008, 03:42 PM
  3. Cold Storage Calculations
    By HAROON in forum Fundamentals
    Last Post: 29-03-2007, 10:13 AM
  4. Cold Storage Unit Selection
    By Sheej Sagunan in forum Technical Discussions
    Last Post: 20-07-2006, 09:28 AM
  5. Cold Storage Design
    By abbasi in forum Technical Discussions
    Last Post: 06-01-2005, 07:17 PM