    Mar 2006
    Philippines
    124
    Lightbulb Back Pressure Valve
    Hi all,
    Somebody has idea the application of back pressure valve (ex. PM3 of danfoss)?
    Is this applicable on glycol system?
    Jun 2001
    N.Ireland
    1,630
    Re: Back Pressure Valve
    Hi Guapo
    The Danfoss PM3 is a modular valve, the PM3 is a 3 Port main valve with room for 3 pilot valves. PM valves are now being replaced by Danfoss, with the ICV range, same pilots, but an improved main valve, better part load performance, less bounch open - closed due to the v ports in the barrel around the gas entry point.
    I have used the PM3 on evaporators as pressure regulators to stop fluid freezing, or as crankcase pressure regulators to stop compressor overloading on hot start-ups
    Kind Regards. Andy.
    Aug 2005
    5,302
    My first question is... why is the back-pressure regulator being added?
    It will certainly work on a glycol chiller or water chiller for that matter.
    If the valve is being added to keep the evaporating temperature of the chiller at a higher pressure to prevent freezing, I suggest you might have other problems that should be investigated.
  1. back pressure valve in chiller
    By vinod in forum Air Conditioning
    Last Post: 12-06-2006, 06:29 PM
  2. Compressor back pressure rating
    By Cary in forum Fundamentals
    Last Post: 05-12-2004, 08:42 AM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Last Post: 13-07-2004, 08:28 PM
  4. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Last Post: 31-07-2001, 11:43 PM