Results 1 to 10 of 10
Thread: Is the TEV mis sized?
Threaded View
-
05-03-2006, 12:11 AM #10
Re: Is the TEV mis sized?
"When it cycles on the presure goes from 82 to 58 then rises to around 65 then a bigsurge down to the off cycle pressure."
Hmmm.. quote buttons didn't work. No matter. In saturated temperatures, you have "It goes from 36 deg F to 22 deg F then rises to around 26 deg F then a big surge to the off cycle. This would make a wonderful Professor Sporlan or Fridgetech challenge. Not moisture, because you can force it to run and achieve temperature. I have to assume if you are achieving temperature and not mentioning that you short cycle, that the compressor is not badly sized.
What on earth is a big surge to the off cycle? Forcing it to run makes everything work okay? What is the time-line? A graph of temps and pressures would likely tell the story. We risk a bad observation on your part, Ken. But nonetheless,
Nice puzzle!
Similar Threads
-
How is a filter drier sized
By kengineering in forum Technical DiscussionsReplies: 2Last Post: 08-08-2006, 05:00 AM -
Need a correctly sized valve
By Abe in forum CommercialReplies: 2Last Post: 26-10-2005, 08:42 PM -
Capacitor under sized
By acman in forum Technical DiscussionsReplies: 2Last Post: 22-09-2004, 02:55 PM -
A/C calculations
By Latte in forum Air ConditioningReplies: 37Last Post: 20-02-2004, 10:18 PM -
Ambient and Condensing.
By kfjoe in forum FundamentalsReplies: 9Last Post: 07-02-2004, 04:31 AM