23-02-2006, 06:46 PM #1
Cap wires melted
Got called out to 2 LG B3660HL ceiling casette systems in the same building because of not cooling. I found that the run wires from the compressor to the capacitor was melted off at the cap end on both seperate units. Also across the cap is a P.T.C device, what is this for Before I replace the caps and wiring has anyone come across this before
-
23-02-2006, 07:10 PM #2
Re: Cap wires melted
Any chance of a photo?
-
23-02-2006, 09:03 PM #3
Re: Cap wires melted
Originally Posted by MickveeNoah had to leave the dinosaurs behind as they would've sunk the boat.
-
24-02-2006, 12:26 AM #4
Re: Cap wires melted
PHTO0239.JPG
Originally Posted by frank
-
24-02-2006, 03:03 AM #5
Re: Cap wires melted
Originally Posted by Mickvee
-
24-02-2006, 10:21 AM #6
Re: Cap wires melted
Thanks for that.
I have checked the comp with a megger and checked the windings resistants and checked out OK. I have an annie analyzer, so I will check if the compressors are jammed. How would you test an PTC
-
24-02-2006, 06:10 PM #7
Re: Cap wires melted
LG again....aaaaaaaarrrrrrrrrrrrrrggggggggggghhhhhhh
-
24-02-2006, 09:31 PM #8
Re: Cap wires melted
Mickvee
Did you test the voltage on site?
-
24-02-2006, 11:39 PM #9
Re: Cap wires melted
Hi
Yes tested supply voltage and was within normal limits, but they have had power surge in the past. The cap tests open circuit, and is rated at 50uF & 370/400 VAC.