Results 1 to 9 of 9
-
22-02-2006, 08:45 AM #1
air cooling and heating coil test
Hi Sirs,
I need to set a test room(higher precision) for air cooling and heating coils heat transfer measurement. I check ASHRAE 33-1978 is for it. But I don't have it on hand. Who have similar experience to test air cooling coils to give me some suggestions:
I want the test system can automatically check and keep the temp/humidity/presure etc data in PC. i'm new to this tech. pls offer me a hand
best regards
LC
I hear...I forget;I see...I remember;I do...I understand
-
22-02-2006, 04:40 PM #2
Re: air cooling and heating coil test
LC,
Here are some sources for you to review.
http://www.ni.com/dataacquisition/
and,
http://www.ni.com/labview/
One of the problems which I think you will find is the area of providing uniform air velocity over the coil face. This will require some investigation of duct work losses and system effects to provide a uniform face velocity.
Here are some links for fan system effects.
http://www.greenheck.com/technical/f.../00apr_eng.pdf
http://www.greenheck.com/technical/t...ide/system_eff
http://ateam.lbl.gov/design-guide/DG...stemeffect.htm
I once looked at this problem for air cooling coils in refrigeration use. The links for the data acquisition hardware/software above are from the company I investigated for this purpose.
I wanted to record the live data into a computer program and have the program do all of the calculations to improve the validity of the data and calculated performance of the cooling coils.
Unfortunately, the project did not develop since it was not important enough and would cost money.
-
22-02-2006, 05:18 PM #3
Re: air cooling and heating coil test
One of the problems which I think you will find is the area of providing uniform air velocity over the coil face. This will require some investigation of duct work losses and system effects to provide a uniform face velocity.
-
22-02-2006, 06:48 PM #4
Re: air cooling and heating coil test
I scanned this information for you, coming from a very old Kuba catalog.
You just have to switch page 1 and 2, I scanned it not the right way and you will also need to turn sometimes a page.
I hope it's usefull for you.
For the registration and logging of all the parameters you describe, we use the loggers form Picotech (UK)
They're cheap, very reliable and extremely fast.
Have once a look at www.picotech.com
Their software is for free, including all the updates.
Litlle problem while scanning the Kuba papers and typing this message: file is to big to post (+/- 220 K) unless Dez can allow for once a larger upload.
There was last a suggestion to download it from another location.
PLease help.Last edited by Peter_1; 22-02-2006 at 08:25 PM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
22-02-2006, 07:15 PM #5
Re: air cooling and heating coil test
Frank,
I am showing my ignorance here, but what is an equalizing grid? The air side of the system is not my strongest area.
Thanks
-
22-02-2006, 08:28 PM #6
Re: air cooling and heating coil test
Originally Posted by US Iceman
An equalizing grid is a sheet (for want of a better word) of perforated metal that sits across the duct, coil, grille etc. As the air volume hits the sheet the air is forced or drawn through the small regular holes. It acts to "eqalize" the flow across an area.
If you select a sheet with really small holes then the equalization is increased but the resistance is also increased. If you choose a sheet with larger regular holes then the air has less resistance to the flow and the effect is somewhat less efficient.
We used a perforated sheet with holes of 8.5mm on a pitch of 18mm recently in an aidiabatic cooler where the air flow was 4.5m3/s. The air was delivered into the cooler in a 900 dia duct by a square to round transition on to a wetted cell 1800 high x 1500 wide. The equalizing sheet allowed the air volume to be spread quite evenly over the whole wetted surface and not just through the middle section.
Try typing equalization grid into Google. Most of the hits refer to grilles or louvres but you'll get the idea.
-
22-02-2006, 08:33 PM #7
Re: air cooling and heating coil test
Thank you for the answer Frank. I have seen these before on a built-up central station air handler I used for an egg breaking plant.
I'll be darned if I can remember the name of thing, but after I read your description I immediately knew what your were describing.
Thanks for the excellent answer.
-
22-02-2006, 08:35 PM #8
Re: air cooling and heating coil test
My pleasure
-
23-02-2006, 01:15 AM #9
Re: air cooling and heating coil test
I wanted to record the live data into a computer program and have the program do all of the calculations to improve the validity of the data and calculated performance of the cooling coils.
Unfortunately, the project did not develop since it was not important enough and would cost money.
For the registration and logging of all the parameters you describe, we use the loggers form Picotech (UK)
They're cheap, very reliable and extremely fast.
I'm deep grateful for all of your kind help.
best regards
LCI hear...I forget;I see...I remember;I do...I understand
Similar Threads
-
underfloor heating and cooling
By Lc_shi in forum New TechnologiesReplies: 19Last Post: 11-12-2009, 12:22 PM -
Evaporative Condenser in reverse cycle
By Friobernal in forum IndustrialReplies: 6Last Post: 16-04-2009, 02:06 PM -
How to controll Logarithmic Mean Temperature of evaporator
By Josip in forum Technical SpeculationsReplies: 14Last Post: 19-08-2006, 12:15 PM -
radiant cooling and heating issue
By Lc_shi in forum FundamentalsReplies: 2Last Post: 29-05-2006, 08:34 AM -
Heating / Cooling Control
By walden in forum ElectricalReplies: 11Last Post: 16-04-2006, 01:20 PM