    Hygroscopic POE oil



    Sorry for opening another thread, hopefully you won't hate me but I still have plenty to learn in this journey.
    Unfortunately I misplaced a cap on my compressor (1/3 HP R290 freezer compressor) and realized some days after as the inlet was completely open. I'm afraid that the POE oil mighy have been contaminated now, so I was wondering what I should do. I've tried pulling a vacuum to 800 micron, and it didnt seem to be rising a lot after that, but I've read that POE oil is very difficult to remove humidity out of, so a vacuum might not be enough. Should I swap it for new oil? Also, I realized I have a normal nitrogen tank, not a "dry nitrogen" one. Should I be afraid to reintroduce the same problem once I'll pressure test the system?
    Thank you!



  2. #2
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    51
    Rep Power
    2

    Re: Hygroscopic POE oil

    Oh, thinking about it, if I added a sight glass, would it show as "wet" if the oil was still contaminated after the final vacuum?

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,365
    Rep Power
    39

    Re: Hygroscopic POE oil

    kay86,
    If open to atmosphere, no good.
    Change oil with new oil that has never been opened.
    Change filter drier, if not already.
    Check with your supplier about the nitrogen quality.

  4. #4
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    51
    Rep Power
    2

    Re: Hygroscopic POE oil

    Thank you!

  5. #5
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    51
    Rep Power
    2

    Re: Hygroscopic POE oil

    Hey, little follow up question. I've emptied out the compressor but I've only managed to recover 130ml, while the specifications say 180ml. I also flushed with nitrogen to make sure most of it would come out. Should I put back 130ml or the whole 180ml now?
    Compressor was never installed so it's impossible it got lost somewhere in the system. Thank you

  6. #6
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    463
    Rep Power
    17

    Re: Hygroscopic POE oil

    Hi kay86,

    It might take a bit longer to get a good reply from the other forum members, theres a lot of posts by spam bots clogging up the "Whats New?" page. Which I think is the page most forum members check for new posts.

    For me, I would probably put in what I took out. So the 130ml. And then once the system is running, keep an eye on comp temps and noise. 50ml difference seems relatively large amount to go missing?

    Cheers

  7. #7
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    51
    Rep Power
    2

    Re: Hygroscopic POE oil

    Thank you Sean, I will keep monitored both amperage and themperature of the compressor.

  8. #8
    Join Date
    Jan 2023
    Location
    India
    Posts
    2
    Rep Power
    0

    Re: Hygroscopic POE oil

    Hi Kay86:
    I worked for a compressor mfr. before. We can't get entire oil out of a compressor. Reason is the compressor is run tested by the mfr. for few seconds before packing. It spreads the lub oil over mechanical parts: cylinder, muffler etc. The lubrication oil is churned at high speed (2 pole speed). This creates oil mist within compressor coating entire internal shell and also the motor windings. This qty of oil which wetted the internal surfaces and motor windings won't come out. The % may look large in small capacity compressors. That is normal. The % will be small in larger compressor having 2 or 3 lit oil.
    When in doubt about nitrogen moisture content for leak test, using a drier in the nitrogen charging line could be tried. I do that "when in doubt".