Problem with commercial refrigerator! Mist like in sight glass???
Hi,
I have problem with one commercial refrigerator with danfoss 120F0002 external compressor, before few days it was fully charged with 404A and oil and now it generate more cold air but also it generate too much noise and when is very hot outdoor it sometimes stop to work many times because pressure switch power it off!
Also when I check sight glass almost immediately after compressor start inside it look like mist, please check video:
https://files.fm/f/xp53w3zda
What you thinking where is problem?
Thanks.
-
05-07-2022, 12:11 AM #2
Re: Problem with commercial refrigerator! Mist like in sight glass???
That sightglass looks like froth which shows a gas shortage, does it clear after running for a short while?
Why was the gas replaced, was there a leak and if yes was it repaired?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
05-07-2022, 01:06 AM #3
Re: Problem with commercial refrigerator! Mist like in sight glass???
No, it stay all time like you can see in video, only few seconds after start I can see something like liquid if I good remember...
Yes, gas leak is reason and they fixed it (I hope), some tiny hole on some valve...
It now working good (cooling is very good) but noisy (compressor generate a lot vibration) but when outdoor temperature go up pressure switch power it off/on/off/on...and also sight glass do not look good...
They said that I have this problem because I have undersized condenser but I do not now is it true...
-
05-07-2022, 02:00 PM #4
Re: Problem with commercial refrigerator! Mist like in sight glass???
It could be a faulty expansion valve, there are a number of possibilities unfortunately which are hard to see from here.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
05-07-2022, 04:56 PM #5
Re: Problem with commercial refrigerator! Mist like in sight glass???
Well for me also something look very bad because compressor sound like working at very high load with too much vibrations and also using a lot more power than usual...also in just few seconds I have very hot air from condenser.
-
05-07-2022, 08:49 PM #6
Re: Problem with commercial refrigerator! Mist like in sight glass???
Condensor coil clear and fan working?
-
05-07-2022, 10:28 PM #7
Re: Problem with commercial refrigerator! Mist like in sight glass???
OFN in the system following recharge?
-
06-07-2022, 01:36 AM #8
Re: Problem with commercial refrigerator! Mist like in sight glass???
Yes, condenser is clear and fan working!
If I good know they not used OFN in the system before recharge...
-
06-07-2022, 07:20 AM #9
Re: Problem with commercial refrigerator! Mist like in sight glass???
Did they evacuate the system propourly?
-
07-07-2022, 09:50 AM #10
Re: Problem with commercial refrigerator! Mist like in sight glass???
Well, I`m sure that they did it...
Can problem be orifice for expansion valve? They used this:
https://store.danfoss.com/en/Climate...ice/p/068-2006
Compressor 120F0002!