Daikin RZQ100L9V1B
Daikin outdoor unit RZQ100L9V1B on R410A gas had circuit breaker tripped,reset and tested.
Indoor fan works ok but outdoor unit refuses to start.240v phase and variable comms normal.
Fuse FU6 on pcboard should be 240vac but i get 4vdc.Checked fuse for continuity and swapped
with an identical unit but no difference.
Compressor does not test down to earth has anyone had this fault.
-
31-03-2022, 08:24 AM #2
Re: Daikin RZQ100L9V1B
Does it work in Emergency mode?
-
31-03-2022, 10:58 AM #3
Re: Daikin RZQ100L9V1B
No,nothing works.
-
31-03-2022, 12:24 PM #4
Re: Daikin RZQ100L9V1B
2.2 Equipment does not Operate
Applicable Model - All models of SkyAir series
Error Detection Method -
Error Generating Condition -
Supposed Causes
Fuse blown or disorder of contact in operation circuit
Faulty operation switch or contact point
Faulty high pressure switch
Faulty magnetic switch for fan motor
Activation or fault of overcurrent relay for fan motor
Faulty overcurrent relay for compressor
Faulty compressor protection thermostat
Insufficient insulation in electric system
Faulty contact point of magnetic switch for compressor
Malfunction of compressor
Defective remote controller or low batteries (wireless)
Check if address is set correctly on wireless R.C.
-
03-04-2022, 09:06 PM #5
Re: Daikin RZQ100L9V1B
Thanks for the info i will check this out next time i am on site.