Thread: Screw Chiller commissioning
-
10-01-2006, 02:13 AM #1
Screw Chiller commissioning
I wondered if anyone had a checklist or form for chiller commissioning. Well to be exact it's actually the water pump in the hydraulic system I need the checklist for, so I can be sure I haven't missed anything out.
Thanks
PS One of our guys had a look at a centrifugal fan on an air handler this morning, and says the airflow is really low. He's checked filters and everything else. I think the motor might be turning in reverse. Any other ideas ??
a problem shared is a problem halved
-
10-01-2006, 02:21 AM #2
Re: Screw Chiller commissioning
If the fan does not have inlet dampers I would check the following.
The first point is what you suggested. Fan rotation.
Bad belt conditions (cracked, glazed, etc)
Or, see if the fan has dirt built up in the vanes. I have seen a lot of centrifugal fans that accumulate dirt in the vanes. This can drastically reduce the airflow capability of the fans. It is not however much fun to clean these.
Is the air system a constant volume system or variable volume system?
-
10-01-2006, 02:51 AM #3
Re: Screw Chiller commissioning
Hi US Iceman
Variable system. The main thing I need your assistance with is commissioning the water (hydraulic system) pump. I guess the main thing is flow and return temps and pressures.
Many Thanks
Jamesa problem shared is a problem halved
-
10-01-2006, 09:16 AM #4
Re: Screw Chiller commissioning
Wish I had the time. If you send me the details then maybe it might be worth doing.
a problem shared is a problem halved
-
10-01-2006, 07:20 PM #5
Re: Screw Chiller commissioning
US ICEMAN
Check your PM'sa problem shared is a problem halved
-
10-01-2006, 11:05 PM #6
Re: Screw Chiller commissioning
Airflow:- Have you checked for dropped fire dampers ?
Water Pump:- Check electrics, check rotation, check valves, check water in system and all air out of system. Get flow data for commissioning valves and design flow rates. Check pump head against pump curve. Check running current. Balance system, record readings.
Now start chiller but only if water flow rate is correct.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
10-01-2006, 11:12 PM #7
Re: Screw Chiller commissioning
Had a centrif fan once that had been taken out to change bearings and then put back in upside down , ran for a year and 4 maintenances before it was spotted
Al
-
11-01-2006, 01:19 AM #8
Re: Screw Chiller commissioning
Brian thank you.
The only info I need is for the hydraulic pump, because I can't start up until I've got the water flow balanced. That should be fine. Many Thanks for the info.a problem shared is a problem halved
Similar Threads
-
York Millenium Screw Chiller
By iceman007 in forum Industrial CompressorsReplies: 26Last Post: 15-01-2011, 11:56 PM -
flooded evaporator in screw chiller
By Lc_shi in forum Technical DiscussionsReplies: 25Last Post: 05-07-2010, 05:37 AM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
Mcquay PES Flooded Water Cooled Screw Chiller
By Brian in forum Technical SpeculationsReplies: 4Last Post: 05-07-2006, 09:43 PM -
York Open Drive Screw Chiller
By Cofreth in forum Air ConditioningReplies: 4Last Post: 24-10-2005, 02:17 PM