Thread: Mycom 200sud-me
04-07-2019, 01:49 PM #1
Mycom 200sud-me
Hi there,
I need documentation and spare part list for Mycom screw compressor, model 200SUD-ME.
Thanks in advance for help.
BR
04-07-2019, 07:22 PM #2
Re: Mycom 200sud-me
Try these links
http://www.bowmanrefrigeration.com/u...compressed.pdf
https://www.hosbv.com/data/specifica...0250%20VSD.pdf
screw overhaul manual not exactly the same, but thrust bearings etc the sameLast edited by RANGER1; 04-07-2019 at 08:13 PM.
08-07-2019, 11:45 PM #3
Re: Mycom 200sud-me
can you send me preventive maintenance manual for 200VLD
09-07-2019, 07:49 PM #4
24-09-2019, 10:27 PM #5
Re: Mycom 200sud-me
thank you RANGER1 for your continuous support i hope this post finds you well
please my MYCOM screw compressor 200VLD reach 50000 running hours and i would like to know the maintenance that i should apply in this time
thank you
25-09-2019, 01:07 AM #6
Re: Mycom 200sud-me
http://www.mayekawamma.com/pdf/SCV_I...20tornillo.pdf
mre212 in manual 5.6 to 5.9 is a fair indication of what needs to be replaced.
Your machine may not have Variable Vi in which case a guide block & pin may need inspection.
In general 50,000hrs would always replace following.
Gasket & “0” ring kit
shaft seal assembly
thrust bearings
locknut & washer kit
main & side bearings
balance piston & sleeve
guide block & pin
indicator “V” ring seal
unload piston cap seal
machine then good for another 30 t0 40,000 hours.
Will find in’s a better document in next few days