07-06-2019, 12:30 AM #1
condenser heat rejection
please for your help i have air cooled condenser but no data please i need to know the cooling capacity of it ?
thank you
-
07-06-2019, 10:21 AM #2
Re: condenser heat rejection
If you could put the make and model details up, we mioght have a better chance of helping you.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
07-06-2019, 02:46 PM #3
Re: condenser heat rejection
i don't have data. can i calculate The heat rejection of an air cooled condenser from this equation :
Qrej = U · A · LMTD
-
07-06-2019, 05:21 PM #4
Re: condenser heat rejection
Do you have any data on the expansion valve make and model? This might give you a rough guide.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
07-06-2019, 05:48 PM #5
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 674
- Blog Entries
- 1
- Rep Power
- 19
Re: condenser heat rejection
Hi
Please measure the length of pipes and dia of that with how many fine has in one inch and size of fins
Also nomber of fans with espification of that
-
08-06-2019, 07:49 PM #6
Re: condenser heat rejection
Coil length =2743 mm
Coil Height =1067 mm
Number of rows =3
pipes diameter = 10 mm
Fins per foot (Alu slit fins) =192