    12kw 6000 liters Waterchiller pulldown time
    customer has a small 12kw waterchiller they want to hook onto there 6000liter uninstalled plastic buffer tank, I dont have any flow rates but ive been trying to work out how long it would take to pull down from 20deg to 7degC tank only no other heatload - doesnt have to be accurate just a ruff idea but I am struggling to find a method, can anyboy help out or point me in the right direction
    thanks
  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    463
    Rep Power
    17
    Re: 12kw 6000 liters Waterchiller pulldown time
    http://processheatingservices.com/wa...me-calculator/
    or very roughly,
    specific heat of water 4.18 KJ/kg k
    1 Kg for 1 Litre of water
    12 KJ/s cooling from chiller
    13 degree temp change
    Q=m x c x change in temp
    Q=6000Kg x 4.18 KJ/Kg K x 13 degrees
    Q=326040 KJ
    Time taken with 12 Kw of cooling,
    326040 KJ / 12 KJ/s / 60 seconds / 60 minutes = about 7.54 Hours
    Lots of stuff not taken into account for though.
  3. #3
    Join Date
    Feb 2005
    Location
    New Zealand
    Age
    43
    Posts
    26
    Rep Power
    0
    Exactly what I was after, thanks very much!
  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    674
    Blog Entries
    1
    Rep Power
    19
    Hi
    the actual time is more than 7.54 h
    you lose a lot of energy in plastic tank and piping and....
  5. #5
    Join Date
    Feb 2005
    Location
    New Zealand
    Age
    43
    Posts
    26
    Rep Power
    0
    Quote Originally Posted by mbc View Post
    Hi
    Thats okey we are just going for rough numbers, we also have 15 hours up our sleeve to pre chill the tank, I was thinking more of around 25kw but in this case they have an old 12kw system in storage we can temporary install fist and go from there