    Daikin EWAQ480F Chiller
    Can any one help me with this chiller, its the first time ive worked on a daikin chiller.
    i had the call for the chiller not working at all, when i arrived the controller had 2 alarms which was +C2 OFFMTRPROTECT and +C1 OFFMTRPROTECT
    After further investigation i found that one of the 80amp fuses had blown on circuit 1, i removed the fuse and took the compressor offline so circuit 1 is currently running on 2 compressors.
    After about 1/2hour of running i get the +C2 OFFMTRPROTECT alarm again and it shuts circuit 2 down, i have looked online and im not able to find what the fault code is or means.
    The controller is also asking for a password which we dont have (just taken site over) without calling daikin applied out to investigate is there anyone on here that has experience or knowledge of these chillers?
    Jun 2006
    South Coast
    278
    Re: Daikin EWAQ480F Chiller
    I would try 1234 for the password
    As for the alarm don't know can't see it in the iom possibly compressor or fan trip.
    Gibbo
    Jun 2011
    Australia
    44
    336
    22
    This document has done the rounds, I’m thinking it was originally compiled by one of the members here
    http://www.frigoristes.fr/getfile.ph...20de%20GEG.pdf
    495
    Try 5321 if it's microtec 3 Siemens controller, I think the motor protection module has shut it down, the compressor motor might be getting hot or some other safety is linked with the protection module
    Apr 2016
    43
    1
    6363: Service password
    Feb 2017
    112
    9
    Thanks for the advice, sadly i didnt get chance to go back to site to try this out but they have got the issue sorted.
    It was a faulty thermistor on circuit 2 compressor, thanks again for everyones help and advice.
    Rik
    Thanks for the update.