    Saturation temperatures
    When looking at saturation temperatures what “rule of thump” are you guys using?
    Saturated condensing temperature 10-15’c above ambient
    saturated evaporating temperature 10’c below space temp ( cold rooms/ freezers)
    Just curious what you guys are using.
    thanks.
    May 2012
    59
    1,528
    Re: Saturation temperatures
    With air cooled
    condenser is 15k above ambient and evaporator is 10k lower than air off.
    So rule of thumb. Condenser 15 higher than air on, evaporator 10 lower than air off.
    Rob
    Nov 2013
    Read this on this forum not sure who posted it
    Here are some figures :
    Tai ----- air entering temperature
    Tao -----air outlet temperature
    Te ------Evaporating temperature
    Twi ------water entering temperature
    Two-------water outlet temperature
    Tc---------condensing temperature
    Air conditioning (evaporator) :
    Tai-Tao = 8 to 10 °C
    Tai-Te=16 to 20°C
    Tao-Te=8 to 10°C
    Refrigeration (evaporator) :
    Tai-Tao = 3 to 5 °C
    Tai-Te=5 to 10°C (evaporator TD) take low TD for high relative humidity
    Tao-Te=3 to 5°C
    Water Chiller (evaporator) :
    Twi-Two=5°C
    Twi-Te=10°C (evaporator TD)
    Two-Te=5°C
    Air cooled condenser :
    Tao-Tai=5 to 10°C
    Tc-Tao=5 to 10°C
    Tc-Tai=10 to 20°C (condenser TD) take low TD in design for hot climate so the condenser will be bigger.
    Water cooled condenser :
    Two-Twi=5°C
    Tc-Two=10°C
    Tc-Twi=15°C (condeser TD)