    Low side maximum pressure
    Hi guys,
    I am relatively new to the industry, having around 5 years experience but do have a good understanding of Refrigeration and how it it all works.
    However no matter who I seem to ask they never give me the definitive answer to what I’m after?
    I’m basically going through Victoria Universiry in Australia to get my skills assesed, however the questions they are asking I believe I know the answer but nobody is saying that’s the definitive answer, which is what I would need to know.
    They are asking, What is the expected maximum pressure the low side may be subjected to? Keep in mind that pressure on the low side is higher when the system is not operating. This would be for both Air Conditioning and Refrigeration
    Is this basically determined after you’ve accurately charged the system to the correct weight, then measured the pressure on your gauges after the system is off, or am am I being stupid and missing something here?
    I presume maximum pressure the high side would be calculated to 15 degrees over ambient temperature in the condenser?
    I just want to be accurate in my answers and have someone that actually understand and discuss my answer with?
    I Would greatly appreciate your answers
  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Re: Low side maximum pressure
    I would go for maximum standing pressure at 55°C as it could be a simple capillary system with the condenser coil sitting in full sunshine.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    674
    Blog Entries
    1
    Rep Power
    19
    Hi
    in brief answer in ideal system:
    In suction
    suction Temp. = room temperature - (6 to 8)
    suction Temp. = comes Gage pressure we read on our Gage and look for gas chart .
    when your system is working your suction pressure is lower than when your system stopped
    when your system stopped your pressure equal with pressure comes from your room temp.
    but in condenser
    condenser pressure :
    Air cold condenser :ambient temperature + (10 to 15 depend on design ) = condenser temp. ( Gage pressure on condenser from gas chart )
    when your system stop your discharge pressure comes down because your discharge temp ( condenser temp.) comes to ambient temp.
  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,365
    Rep Power
    39
    I just think max ambient temperature, because if off can’t get any higher than ambient or room temperature.
    If system just turned off, evaporator would have been working & area cool, equalisation occurs.
  5. #5
    Join Date
    Aug 2014
    Location
    England
    Posts
    3
    Rep Power
    0
    Thanks a lot for that! Simple I know, I just wasn’t considering the ambient temperature. I was looking too far into the question I overlooked the basics.
    If you haven’t any colleagues to discuss things with, you can easily overlook things!
    Stupid Pom is what the usual response is. They even call a flared conduit pipe end a bell end! They didn’t understand why I thought it was funny!
  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,365
    Rep Power
    39
    Quote Originally Posted by mfurze View Post
    Just remind them of Australian cricket team cheating, get some mileage out of that��
  7. #7
    Join Date
    Aug 2014
    Location
    England
    Posts
    3
    Rep Power
    0
    Trust me I have! They can’t handle the banter
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts