    Mitsubishi Mr Slim
    Hi guys
    I have a mitsubishi PUHZ-P125YHA with 2 high wall units.
    Compressor runs for 10 seconds and unit turns off no fault. Fans don’t run. I have a hand held remote. I used the self diagnosis function which came up with 8 beeps . P8 , not sure if this is an old fault.
    Any thoughts
  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Re: Mitsubishi Mr Slim
    It could be P8 or U8 depending on the beeps, have you checked the outdoor unit errors?
    Service manual here.... http://bit.ly/2Htkewr
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  3. #3
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21
    Thanks Brian,
    The problem was I’d been work for 12 hours, it was dark and I was hungry , Faulty fan motor is the end result .
  4. #4
    Brian_UK's Avatar
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Well done buddy, that's the U8 then.
    Retired March 2015
  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47
    I don't know many who cannot relate to that scenario.
    Well done.
    Grizzly
    Despite the High Cost of Living it still remains Popular!
  6. #6
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21
    Cheers guys , thanks for the help