    Carel evd
    Hello,
    I have a Carel EVD expansion valva electronic.
    I have a low pressure and a high pressure probe, and suction and liquid sensor ntc.
    I have all the time a wrong value with the high pressure probe. The others are ok.
    The high pressure probe is parallel on the low pressure, and S3.
    The probe is correct. Try with another is the same.
    Carel dont answer me.
    Anybody an idea?
    Aug 2007
    Russia
    140
    22
    Re: Carel evd
    Is your connection like that? Are the S1 and S3 probes of the same type? What is the probe output voltage?
    Nov 2005
    belgium
    61
    Re: Carel evd
    S1 and S3 are the same type: ratiometric
    Re: Carel evd
    Is the controller set to match the sensor?
    Nov 2005
    belgium
    61
    Re: Carel evd
    Yes.
    The supplier has a lab box with the valve and sensors. He has the same problem.
    Changing the parameters sensor active or not doesnt help
    Re: Carel evd
    Okay, so if the components and cabling are correct then we need to look at the mechanics.
    How does the sensor reading compare with actual pressure?
    Is the sensor connection to the pipework good? By this I mean is the valve pin depressed properly by the sensor when it is screwed on. Test it by fitting a tee-piece to the access port and fit your sensor to test both items.
    Aug 2007
    Russia
    140
    22
    Re: Carel evd
    Can you measure the probe DC output voltage between S3 and Gnd?
    Nov 2005
    belgium
    61
    Re: Carel evd
    Yes. The sensor is correct. It measure 33 bar, we have R404A. The real pressure is 17 bar.
    It is strange that on the lab box we have the same problem. The lab box is from Carel.
    The valve works very good. I only want the high pressure for reading only.
    Nov 2005
    belgium
    61
    Re: Carel evd
    I will do that this evening (belgium time) if i am back in time (4 calls already and the day just begins).
    Or i do this after x mas.
    Thanks for helping
    Nov 2005
    belgium
    61
    Re: Carel evd
    Quote Originally Posted by narkom View Post
    Thanks for helping
    Re: Carel evd
    Is the correct scale range for the sensor selected and set on the controller?
    Sorry, second question - what are the ranges of the high and low pressure sensors?
    Nov 2005
    belgium
    61
    Re: Carel evd
    The supplier gave me this: low pressure 4-20ma -0,5 / 7 bar high pr 4-20ma 0 / 30 bar.
    In the configuration if i want to change S3 it always go back to “not used”.
    I measure 8,5 V between GND and S3 display shows 33,7 bar. Real i have 17 bar.
    measure: S1. 2,45 V 3,5 bar display
    S2. 2,45 V 6’C display
    S4. 1,65 V 22’C display
    Maybe i have to use 0-5 V?
    The supplier gave me for another installation for low pressure 0-5 V and high pressure 4-20 mA!
    I guess it have to be two of the same sorts, not?
    And wich one, V or mA?
    Probe 4 is in programmation also “not used” and impossable to change.
    And this probe measure good.
    Happy holidays!
    Re: Carel evd
    So you do NOT have ratiomatic sensors, they are 4-20ma sensors.
    Yes, you must use two of the same sensor type.
    Set the controller accordingly.
    Nov 2005
    belgium
    61
    Re: Carel evd
    The both sensors are 4-20mA.
    What is ratiometric? Is this the 0-5V?
    Re: Carel evd
    Yes, see your parameter list that you posted earlier in post #2
    Nov 2005
    belgium
    61
    Re: Carel evd
    I will change the probes next week with 2 0-5V probes.
    Lets see if this is better.
    Nov 2005
    belgium
    61
    Re: Carel evd
    Hello
    Both changed to 0-5V. Now it is ok.
    Thanks a lot.
    Happy new year.
    Re: Carel evd
    Good news, thank you for letting us know.