Results 1 to 29 of 29
Thread: Sab 128 Problems
06-11-2017, 08:38 PM #1
Sab 128 Problems
Hello, I have a Sabroe 128 MK2. The suctiongas temperature is too high and the amp is too low. It should use about 180 amp, it uses 135-150. The suctiongas temperature is +10-20. The rest of the values seems OK. Has anyone in here seen something similar? I find nothing wrong with the mecanics. I dismantled it and put it together again, and the first time I started it, it worked OK. Then I stopped it and startet it again, and the problems came back.
07-11-2017, 03:21 AM #2
- Sep 2009
- Iran
- 66
- 674
- 1
- 19
Re: Sab 128 Problems
put it in manual position
than push up load see what happen
if you capacity goes up and AMPS move to high
you check your setting
if not
check suction filter and all valves
07-11-2017, 04:31 AM #3
Marthe,
Suction, discharge, oil pressures, refrigerant etc would be helpful.
Are pressures normal/ abnormal?
These types of compressors have hydraulically driven suction check valves, so oil pressure & filter condition important.
Also slide valve indication may be out of calibration, as MBC mentions, can you force it to load more?
Is something inhibiting it from loading like motor amps or pressure, check settings.
Check if your readings are correct for transmitters as bad power supply can upset readings as well.
http://www.cooltech.ru/en/spares/sabroe/spiral/sab128Last edited by RANGER1; 07-11-2017 at 07:28 AM.
07-11-2017, 09:40 AM #4
I have checked the suction filter. It was OK. I also tried to put it in manual position. When I pushed upload, the capasity went up to 100 %. But the amps did not rise. And the suctiongas temperature did not go down. Every other values were OK, such as oilpressure, oiltemp, suctionpressure etc. It seems like the compressor shows 100 % capasity, but only runs in 10-20% capasity. The slide calibration is also OK. I think there might be someting wrong with the slide, showing 100 %, when it maybe is 10-20%, I don`t know.
07-11-2017, 08:37 PM #5
marthe,
Do you have manual or auto Vi, if auto is it working.
You think slide is 100% but can you energise load solenoid or use magnet to see if it can do anymore work?
Is POV bypassing (discharge to suction), as maybe could feel of hear it.
08-11-2017, 04:14 AM #6
- Sep 2009
- Iran
- 66
- 674
- 1
- 19
if don't have manual of that inform me I will send it to you .Last edited by mbc; 08-11-2017 at 05:32 PM.
08-11-2017, 10:43 AM #7
I have manual Vi. But there is a set screw in the end of the regulator. I try to find the correct lenght of that.
08-11-2017, 08:36 PM #8
- Sep 2009
- Iran
- 66
- 674
- 1
- 19
there is two REG valves
one for loading
2nd for unloading
close unload one then when compressor is running inergyzed solinod of load by hand very jentilly
and measure AMP. and load
08-11-2017, 08:56 PM #9
The sab128 has a manual Vi if I remember correctly (don't take my word for it) so I would leave that alone unless the compressor has been recently refurbished.
is it controlled by a Unisab controller?
if so it might show 100% capacity when it's not really in full mechanical slide capacity.
The unisab controller while it is good, may figure out that the compressor is in 100% capacity, based on the suction pressure, discharge pressure and amps and will show 100% in the display, but the slide might only be at 30% load...
The unloading solenoid is normally open, meaning it should be energized as long as the compressor is running and click off when it gets a decrease pulse.
the increase solenoid is normally closed, so that one should be energized only when the compressor is getting an increase signal.
Watch in the unisab display if there is an up or down arrow blinking next to the capacity % in the unisab display, if it's showing 100% and there is an arrow pointing up blinking next to it, it means that the Unisab controller is asking for more capacity, every time the up arrow blinks, the increase solenoid will be activated.
if the display shows 100% in the bottom right and there is no up or down arrow blinking, the unisab is saying that the compressor is now at it's max efficiency.
I'm guessing that the compressor is also fitted with a standard Sabroe capacity indicator like this:
lot-2-sabroe-3448-004-capacity-indicator-johnson-controls-new-h3-2107-c9a4c03054bae46eff89c8bd52.jpg
and if you think it is calibrated... you may be wrong
First of, the text has to be level, then you have to do like MBC said, on either side of the increase and decrease solenoids, there are reg valves, close the reg valve on the decrease side and then disconnect the solenoid on the increase side and use a permanent magnet/service solenoid on the increase side to find the true 100% position. this should be done on an already cooled down plant
Then adjust the 100% (max point) using the screw on the front of the capacity indicator.
Because even when you run in manual on the unisab is working in the background and may reduce capacity while you are pushing increase-Cheers-
Tycho
10-11-2017, 12:20 PM #11
The capasity is calibrated. The compressor goes on 100% and everything seems ok. Then suddenly the amps go down from 170 to 140 and suctiongas temperature also rises, apparatently for no reason. It seems to loose capasity and compression. But both the Unisab and the clock show 100 % capasity. It sometimes work, sometimes not.
Is it possible that the capasity is not calibrated when both the Unisab and the clock shows the same? The clock follows the slide mecanicaly, doesnt it?Last edited by marthe1994; 10-11-2017 at 12:24 PM.
10-11-2017, 09:16 PM #12
I have checked the slide, and then capasity, and I changed the capasity regulator valve with another sab 128 and that works fine. The online thing left in my mind is to check the oilcapasity and the screws. The oilpressure seems ok, but can there be a leakage in the screws? I dont know yet. How can I check?
11-11-2017, 01:38 AM #13
Marthe,
Do you have above pictured potentiometer, or the newer type linear position indicator?
If potentiometer like pictured you can loosen 4 screws a bit & turn potentiometer complete with glass clockwise, this will alter reading on Unisab to lower than 100% & you could try to load it more.
If you lock slide valve indicator in one spot, does it stay in same % or move by itself?
If normally open solenoid is damaged it would creep to unload all the time or depending if solenoid seat damaged maybe some of the time.
Make you sure it is calibrated, what have you done to prove it.
Eliminate one thing at a time.
I have a a problem with one at the moment & believe it is damaged magnet driving indicator like in picture.
Have new one on order, hopefully fixes it as magnet slips, leaving indicator at full load , but is actually at full unload.
But if it were your case, why would it unload if capacity is required unless it was the same
as mine & you can't see it unload due to faulty magnets?
Front cover if not assembled properly can also cause rubbing between glass & disc with slot in it to drive potentiometer.
Also so check that it's not backing off on motor amps or high discharge pressure, as these override everything. Check settings & determine if ok.
You also mention in your first post about dismantling mechanics, what did you do exactly.Last edited by RANGER1; 11-11-2017 at 06:52 AM.
11-11-2017, 07:00 AM #14
11-11-2017, 07:06 AM #15
11-11-2017, 07:14 AM #16
Depending on what potentiometer you have it's a magnet on old type in picture supplied by Tycho.
New type is linear position indicator, also magnet.
http://www.hbproducts.dk/en/products...pacity-sensors
http://www.hbproducts.dk/en/products...or-long-stroke
http://www.hbproducts.dk/images/cert...ual-022-UK.pdfLast edited by RANGER1; 11-11-2017 at 07:19 AM.
29-11-2017, 01:57 PM #17
Problem solved.
The guide for the slide that is pressed together with the slide was not good enough connected. Sometimes the factory use glue to hold this together. This glue had been broken so the slide was loose. But not too loose, because sometimes it was fastened, and sometimes not. That is why I had so big difficulties to find the fault. Now I will glue it properly and see what happens. Thanks for all your input and advises. Hopefully it will be a long time till my next problem.Last edited by marthe1994; 29-11-2017 at 02:00 PM.
29-11-2017, 07:05 PM #18
Thank you for the update, hopefully problem resolved.
29-11-2017, 09:31 PM #19
30-11-2017, 04:59 AM #20
30-11-2017, 04:59 AM #21
What on details you want to know?
30-11-2017, 05:28 AM #22
What's the slide?
30-11-2017, 09:02 PM #23
30-11-2017, 09:22 PM #24
Marthe,
We go out of our way to try & help & would like to know exactly what you did to fix it so we can learn from it.
Your answer is to vague to make anything of it.
Do you have a picture, anything?
What is slide, is it slide valve, slide something else, your terminology i do not understand.
Maybe you mean potentiometer, or dial that turns it?Last edited by RANGER1; 01-12-2017 at 12:24 AM.
01-12-2017, 05:27 AM #25
I appriciate all the help I get in here, and I am not trying to be here "for free". I hope I also can help someone, every now and then. But now I understand your questions. I am sorry if I was describing imprecisely. I will try to explain. My english is not allways so good, as I don't know what all the parts are named in english.
By slide I mean the capasityslide that goes in and out under the screw. This slide is connected with the guide, useully pressed together. In my case, it was glued together. Here is a picture20171130_072721.jpg
192 is connected with 190, inside the hole in 190. In my case, these two were not fastened together properly. As I wrote earlier, it was partly tightened. That is why the compressor sometimes worked ok, and sometimes not. The reason for this is that the factory pressed these two parts together with 1 ton pressure. If this was not enoungh, they also glued it, to make it stay fastened. After som time, in my case 20 years, this glue broke, and the capasityslide (nr 190 on the picture) loosened from the guide (nr 192 on picture). Then I had problems with capasity on compressor. Now I put on new glue and press these two together again. Hope this was helpfullLast edited by marthe1994; 01-12-2017 at 06:06 AM.
01-12-2017, 06:12 AM #26
Marthe,
Thanks more clear now, not a simple fault to rectify by the looks of things, much appreciated.
01-12-2017, 06:18 AM #27
01-12-2017, 06:57 AM #28
Hi Marte.
Thank You for an interesting fault topic.
These fixes are what helps us all diagnose future issues.
The non catastrophic type Ie. loose component or wire etc.
Are sometimes the hardest to find but the easiest to fix!
04-12-2017, 11:13 AM #29
Update and correction.
I am sorry. I made a mistake in my reply to Ranger1
It was the Vi-slide that was loose from the guide. What happened was that the Vi-slide was loose, so the capasity-slide pushed the Vi-slide too long in. Then the Vi was wrong.