Results 1 to 24 of 24
Thread: Howden wrv163 lube oil pressure
Threaded View
Re: Howden wrv163 lube oil pressure
PLEH2EREH, is this the same compressor you asked about in an earlier post, that has liquid injection for oil cooling, or is it a different one?
if it has liquid injection, close the oil injection that goes into the side of the compressor completely... It should get enough oil from the connection in the shaft seal area like Ranger says (though personally I nudge the oil injection open 1/2 turn, just to be generous)-Cheers-
Tycho