Results 1 to 12 of 12
Thread: Carel PCO maintenance passwords
-
05-10-2017, 08:04 PM #1
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Carel PCO maintenance passwords
Hi,
I have some units under my maintenance contract with Carel PCO controller witch are experiencing maintenance alarms.
Since these are abandoned by original installer (they gone out of businesses), I am unable to find or acquire original documentation.
Unit in question are from Thermocold and Emicon.
I would appreciate if anyone know what are maintenance passwords of those manufacturers, since original Carel maintenance password is not functioning there.
-
05-10-2017, 08:45 PM #2
Re: Carel PCO maintenance passwords
5321 and higher level 6363...there are others but can't bring them to mind at the moment
-
05-10-2017, 09:12 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Carel PCO maintenance passwords
Thanks man! If you recolect any other, I am all ears!
1234
0123
Is what I have!Last edited by nike123; 05-10-2017 at 09:22 PM.
-
05-10-2017, 09:20 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Carel PCO maintenance passwords
Is it possible to order Carel EEPROM chip with software unlocked, like in Carel PCO available at stores, and only change parameters according to application ( i have no problem to parameter it myself)?
I have two fully functioning PCO boards but with locked software. If I could buy only EEPOM chip and make changes in parameters it would be much cheaper for customer to go that way!
-
06-10-2017, 08:00 AM #5
Re: Carel PCO maintenance passwords
Have you tried 1000
-
10-10-2017, 02:14 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Carel PCO maintenance passwords
Yes, it is tried 1000 and 0123 and 1234!
Also, unit in question have 2 PCO boards. One is master and second one is slave.
When we enter 1234 password on the screen appears question something like second (level?) password!
It appears that 1234 is OK for first level or something like that, but another password is required for 2nd level.
We need to reset compressor maintenance alarm.Last edited by nike123; 10-10-2017 at 08:17 PM.
-
10-10-2017, 03:56 PM #7
Re: Carel PCO maintenance passwords
If I remember right there are three different passwords user,maintenance and manufacturer, your best bet is try and contact emicon as it is there software passwords and not carels
-
10-10-2017, 09:08 PM #8
Re: Carel PCO maintenance passwords
On the York chillers with 1234 level access, the higher access is 4321..have you tried this?
-
12-10-2017, 12:38 PM #9
Re: Carel PCO maintenance passwords
Hi Nike
if you have same 02 units running fine then you can copy that software and past in the other units running with alarm . its very simple ,
jusp purchase carel key connect it with pco , with rj11 connector then you can do copy and paste
key.png
-
04-11-2017, 06:27 AM #10
Re: Carel PCO maintenance passwords
All Carel PCo passwords which I met was between 0100 and 0120. Such as 0100, 0105, 0110, 0113 and 0118
-
04-11-2017, 09:46 AM #11
Re: Carel PCO maintenance passwords
And else one - password for CAREL PLC : Menu setting : 00000 et Menu service : 00121.
-
13-11-2017, 10:08 AM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Carel PCO maintenance passwords
Emicon case is solved by replacing PCO board with another one from similar Emicon, but non functioning (mechanically) unit. I still don't know passwords for Emicon. Termocold case is solved by entering one of passwords listed here on thread, but i cannot remember which one!
It must be related to my age!
Anyhow, thanks to all contributors!