    how to select refrigeration equipments for -18 freezer room
    What is the selection procedure for selection of Compressor, condenser(air-cooled), evaporator, exp valve for R-22 & R-404a refrigerants to use this system for -18 freezer? If my compressor is 20 HP semi-hermetic than what will be evaporator and condenser size.
    Sep 2010
    208
    Re: how to select refrigeration equipments for -18 freezer room
    No. 1, select a refrigeration engineer.
    No. 2, ask him to design your system.
    Aug 2016
    India
    8
    thank you so much for opening my eyes sir.......appreciate the reply..
    May 2012
    59
    1,528
    You are starting at the wrong place.
    You have an engine and you are asking how big is the bus
    that I need to build around it?
    What you should be asking is how many people do I need to move????
    You need to know your product load before you then size the evaporator,
    after sizing the evap to the load you size the compressor to the evaporator.
    Then you size your condenser to reject the heat from both the evap & comp.
    As a rough rule of thumb the compressor will be about a third of the size of
    the evaporator, so a 9kW evaporator would require approximately 3kW of compressor
    and then both 9kW + 3kW = 12kW would be rejected from the condenser.
    Just rough numbers mind and the real system is more complicated.
    Rob